Hi, during kitchen refurbishment, the electrician installed a 4mm cable and 32a breaker for the new induction hob rangemaster oven that is rated at 16.2kw.

Same electrician couldn't connect hook up cooker, so I asked someone else to do it. The new electrician refused to connect up saying it needs a 10mm cable 45a breaker. Both professionals are in disagreement. Would be great to get a consensus here please. I want to use the oven without concern it may trip the breaker (5 induction hobs, 2 ovens and warming drawer)

Thanks
 
Originally designed for three phase supplies at one third of the current ?
Yes, quite common in various European countries. I wish we had it more here, it's much easier wiring a cooker with a 5 core 2.5mm flex.
Yet type approved for use in the UK.

Which body is responsible?
No complaining! It's all part of haRMoniSiNG WiTH EUroPe. Think how wonderful it is that all these changes mean you can now drag your 1200 wide UK rangemaster cooker over to France and wire it into your new home there! How's that for convenience.
 
Think how wonderful it is that all these changes mean you can now drag your 1200 wide UK rangemaster cooker over to France and wire it into your new home there! How's that for convenience.

Extremely convenient once you've paid the export tax, import tax, brexit tax.... 😂
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Ripon
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
4mm cable, 32a breaker for 16.2kw Rangemaster installed by electrician
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
44
Unsolved
--

Advert

Thread statistics

Created
Chris C300,
Last reply from
davesparks,
Replies
44
Views
12,098

Advert

Back
Top