Discuss 6mm main earthing conductor and main bonding conductors in the UK Electrical Forum area at ElectriciansForums.net
P
pistolpete
Been asked to install an extractor in bathroom. Installing 30mA rcd spur outside covering all lighting and ext fan. Obviously notify building control and installation cert. what's people's opinions of listing as a departure from bs7671 on installation cert. obviously recommend upgrade to 16mm. supply is TN-C-S and DNO connected 6mm to service head. Thanks in advance
as far as the earthing is concerned.....then you need to know the size of the bullit in there....and then do the adiabatic for it...
when it comes to the bonding.....as long as its visually good for continued service (and this includes any connections)...and it tests OK...then just note it....it isn`t a fail....although i would personally be recommending it be upgraded...
If its wrong you shouldn't be carrying out any additions or alterations.
If your install is out of zones 1 and 2 you need not notify anymore either!
for what it is worth I decided to ask Elecsa their stance on this recently. In my case I was doing a CU change and the bonding and earth were 6mm (TNCS).
Their response was:
1) Does the adiabatic work for the main earth?
2) Is the bonding in good nick with no signs of overheating?
If yes to both the above then tell the customer it should be upgrade and give a quote. However when the customer refuses the extra cost/hassle crack on and do the work but put a note on the cert that it is undersized but ok and the customer did not want it upgraded.
Which is basically what Glenn said ;)
0.05 is the value given in guide note 3 for the testing of bonding but I would not take it on its own as evidence of good bonding.
Brought this up with Nic Eic engineer, they said if it meets sizing calculated by adiabatic equation note it on cert and notify customer recommended upgrade to main earthing conductor. Thanks for responses
Reply to 6mm main earthing conductor and main bonding conductors in the UK Electrical Forum area at ElectriciansForums.net
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
6K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread). At present the farm is all PME. I believe it needs...