Got called out to a shower tripping which has been recently installed by another spark.
8.5kw shower newly installed on existing 6mm2LSF cable not longer than 10m from single phase DB. Protected by a 40A RCBO Type B
(shower current Calculated at 36.95A @ 230v)
when clamped shower was pulling over 56A with load on at load side.
Shower would run for 10 minutes then trip. I believe this is overload given the reading from the clamp meter.
RCBO would fail to reset instantly with shower load off/ pull cord in the off position
I fitted a 50A mcb for curiosity to clamp the circuit again. Clamp at the db was reading 45A, clamp on load side of shower was fluctuating between 76-81A, the circuit held for over 20 minutea before I switched it off.
Can anyone Shed light on why these reading would be so diverse.