Hi folks,

Just need a bit of advice regarding whether or not neutrals require switching.

- 3 phase board, 3 pole main switch, neutral is un-switched. 416.2 (ii) states that switching of the neutral is not required if the conductor is reliably connected to earth by a low resistance to meet the disconnection time requirements of Ch41. How might I conclude that the resistance is low enough, and therefore the reg has been adhered to?

Couple of extra details regarding the above if required:
  • TN-C-S
  • Zs @ DB is about 0.08 Ohms
  • Continuity measurement between N-Earth about 0.07 Ohms
  • BS88-2 63A fuses

- 3 phase dishwasher, 4 pole rotary isolator requires replacement. Similar situation to above, I'm trying to work out if I can fit a 3 pole and leave the neutral un-switched.

Many thanks in advance!

Tom.
 
In a TN system it's not really desirable to switch the neutral as any failure in this regard will start a fireworks display. The neutral is reliably connected to Earth by a suitably low impedance in a TN system.
 
as above. 4 pole switching generally only required on a TT earthing system.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Advice on 461.2 needed
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
tomlonsborough,
Last reply from
Strima,
Replies
4
Views
2,282

Advert