Just need a bit of advice regarding whether or not neutrals require switching.

- 3 phase board, 3 pole main switch, neutral is un-switched. 416.2 (ii) states that switching of the neutral is not required if the conductor is reliably connected to earth by a low resistance to meet the disconnection time requirements of Ch41. How might I conclude that the resistance is low enough, and therefore the reg has been adhered to?

Couple of extra details regarding the above if required:
  • TN-C-S
  • Zs @ DB is about 0.08 Ohms
  • Continuity measurement between N-Earth about 0.07 Ohms
  • BS88-2 63A fuses

- 3 phase dishwasher, 4 pole rotary isolator requires replacement. Similar situation to above, I'm trying to work out if I can fit a 3 pole and leave the neutral un-switched.

Many thanks in advance!

Tom.
 
In a TN system it's not really desirable to switch the neutral as any failure in this regard will start a fireworks display. The neutral is reliably connected to Earth by a suitably low impedance in a TN system.
 
as above. 4 pole switching generally only required on a TT earthing system.
 
As above, no need to switch the neutral in a TN.
 

Reply to Advice on 461.2 needed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Morning all, I’m scratching my head with this and granted I don’t do a lot of commercial work. Hence I thought I’d ask. Setup is a pub with a...
Replies
12
Views
2K
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock