Wilko

Hi - got a job at an older 2br house to change out fusebox for CU. I haven't pulled the fuse but think it's likely 60A (common in area and place had gas CH and HW), recent smart meter and it's TNCS. It's got 16mm tails and less than 3m between meterbox outside front door and fuseboard at head level just inside. Tails are in good condition from what I can see and I hadn't planned to replace them (?). Meter has seal. Can't seem to recall about fuse seal.

First question - existing tails may not have slack to neatly position them within the new CU, as it's twice the size of the fuse board. If so, I was thinking to install an isolator in the meter box to give a kickoff for new slightly longer 16mm tails as this avoids touching the meter. Sound ok so far?

Next question - do I use metal or plastic for the isolator in the meter box ? If the cutout was inside I'd be using metal, but I'd also probably have a lot more room. Or if it needs new tails should I get Customer to order up an isolator from SSE (who will likely use a neat little plastic one) ?

Any suggestions welcomed, thanks :)
 
  • Like
Reactions: Specialist
Of course you can, but it's the breaking of the seal in the first place is the issue. If you want to go to great lengths of sealing something you haven't broken, that's up to the individual.
 

Similar threads

D
Replies
5
Views
4K
UK Electrical Forum
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
AMD 3,16mm tails and isolating sw for domestic
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
21
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Wilko,
Last reply from
Midwest,
Replies
21
Views
404

Advert