polo1

~
Arms
Dec 28, 2010
1,285
650
688
Glasgow
Business Name
GW Electrical & Security
In case I've missed something- 40a mcb in an old Simplex cu feeding a standalone, plastic cu consisting of a 63a, 30ma rcd as main switch and a 40a mcb. 10mm t&e serving a 9.5 kw Mira shower via a 45a dp switch.
Random tripping of the rcd when the shower is off ( power to the switch internal to the shower, but shower not running).

Rcd ramps at 22ma, x1 & x5 results fine, Zs what you would expect with measured Zdb and length of cable. Insulation resistance 999 on all combinations and resistance of heating tank fine. All connections tight. Cable run in loft is visible, no damage.

I wasn't able to ir test N-E on remaing circuits due to not being able to isolate on this first visit (am going back when house is unoccupied) but any thoughts meantime??
 
Could this be a dodgy neon? Either in the shower or isolator switch?
 
Is there any water dripping /spraying inside the shower cover?
 
Is there any water dripping /spraying inside the shower cover?

Nope, totally dry. Ran the shower for a good 15 mns. No signs of water ingress or leak at inlet.

Interesting point about dodgy neons; shower has two neon, these are only on when the shower is actually running. The 45a switch has one neon, and the switch is typically left in the on position.
 
It could,but the reason would may be apparent, if the lids have been off.

I take it the Simplex has no RCD? What bonding is present,are the other supplied accessories in the bathroom supplied from the non-RCD DB,such as lights,immersion,etc, are there sections of pipework separated by plastic... lots of opportunities for other electrical shananagins :)
 
Have you tried tapping (gently) on the side of the RCD to see if it trips as it may be just so worn that any vibration can cause a trip. 22mA on a ramp test is a bit low (passes but a bit low) so may indicate ease of switching, perhaps?
 
  • Like
Reactions: David M
All, thanks for the responses.
Simplex board has no rcd; all other circuits off this board. Main & equipotential bonding is in place. Ramp test result in op.
Peg, all appears to be copper piping with no plastic connections/inserts.
And yes Richard, I did try tapping on the rcd - I learned that "trick" a good few years ago!
 
How would a dodgy neon trip an RCD?
It was just a thought. I was thinking of a flickering neon causing an inbalance between live and neutral or possibly the sleeving of a neons wires having broken down and allowing shorting to earth.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

polo1

Arms
~
Joined
Location
Glasgow
Business Name
GW Electrical & Security

Thread Information

Title
Another tripping rcd.....
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
polo1,
Last reply from
Had8Lives,
Replies
9
Views
2,936

Advert