Top Cat
Anyone know what the kA of this breaker is? Also on same board i had a 30mA RCD main switch that had a BS number of 4293. Can't find that number should i just put down 61008?
4293 is the BS number for older type RCDs...replaced with BSEN61008....the max times are different....look in GN3 (p) 53 for rated short circuit capacity of MCBs to BS3871
pt1 may mean type 1, equiv. to type B in 60898.