Good Evening Gentlemen,

Please bare with me as I have looked at previous posts and some people have asked similar quistions and got slated for it...

I am wiring an office, it's on the fourth floor of a multi story building! I need to run two supply's to comms cabinets inthe basement. The cable run is under a raised floor so in free air really clipped to the floor! It then jumps into a riser down to the basement on basket on its own again. The overall run is 89 meters my employer seems to think 6mm swa will be fine. And I just wanted to check... I have not worked these figures out in a while but come to the conclusion that I will have 10.39v in my volt drop and rating factors ca = 1. Cg=1. Cf=1. =3 16amp 60898. 16 divide by 3 = 5.33

So could you please guid me whether I am on the right tracks or and if my cables selection is right.....

Many thanks
 
need to know the design current.
 
The PD current has been used here to calculate the volt drop.

But as Davesparks says it is not divide by 3 but by 1 to give a tabulated value of 16 A or less.

6mm² SWA will just about cope with that!

So volt drop OK, current carrying capacity OK.
 
Id be more concerned about the earthing arrangement here been a comm's supply... upgrading the SWA to 4core and larger csa could allow for an extra core to meet the requirements of the functional earthing....

Thats if it is what I think it is?

It be an expensive error to forget the requirements for functional earthing ... again if it is required --- info needed!
 
Last edited by a moderator:
Thanks for the reply's people....

I am gaining access to the comms room tomo so will check the earthing arrangement, but when ever I install power to comms cabinets I run a clean earth back to the incoming earth bar!

Many thanks
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Cable calcs
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
Mr s,
Last reply from
Mr s,
Replies
5
Views
1,149

Advert