Would normal twin and earth be ok for lighting in a home steam room or do I need heat resistant?

It'll be run above steam room on cold side of insulation as regs recommends, but being for lights, obviously end will be pulled through insulation.

Cable to steam generator will be standard 10mm grey cable also or am I looking at some heat resistant 10mm cable?

Thanks.
 
What did your electrician that is designing it say?
 
  • Optimistic
Reactions: Pete999
Steam room? So a sauna then? Classed as a special location. Is this commercial or domestic?
 
Hi - it's a Special Location detailed in Section 703. Cables are mentioned in 703.512.2 and likely you will need cable rated 170 deg C + (silicon based rather than pvc for example).
 
Last edited by a moderator:
Thanks Wilko.

It's domestic.

Yes, I've already seen the regs, all wiring will be on the cold side of insulation (703.52), except the ends of the lighting wires, for obvious reasons.

I'll have to use the silicone based cable for that then I guess.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Cable type for home steam room
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
n180,
Last reply from
n180,
Replies
4
Views
1,609

Advert