How is voltage drop of a circuit normally calculated in the UK? And why are wires 16mm2 and under listed as a single unit, but 25mm2 and over in R, X and Z? How do I work with Z?
 

Attachments

  • wire.jpg
    130.3 KB · Views: 14
in the UK we use tables showing mV/A/m for different cable sizes. e.g. if we have a cable 50m long, 20A, and the table shows 7mV/A/m, then VD = (7 x 50 x 20)/1000 i.e. 7000mV or 7V.
 
pass on that. I never use cables that big
 
For small cables at 50Hz, the ohmic resistance dominates, so it is not important to consider the DC resistance and AC impedance separately. A single figure is used for all applications.

For larger cables with lower resistance, the inductive reactance starts to become significant on AC, so the voltage drop arising from each effect, and their vector sum, is given. For DC, the r figure alone would be used. For AC, the impedance. By tabulating both the reactive and resistive contributions, the total drop for a load of known non-unity pf can be calculated (where the drop is displaced in phase from the line voltage) for greater accuracy.
 
But even for small cables, doesn't load power factor effect voltage drop considerably? Does DC resistance or AC resistance give the worst figures vs AC reactance (Z)?
[automerge]1575993418[/automerge]
Here is the NEC's Table 9. Reactance, even load power factor when known is taken into account for smaller conductors down to 2.08mm2.
 

Attachments

  • table 9.jpg
    473.9 KB · Views: 10
  • Table 9 #2.jpg
    109.7 KB · Views: 8
Last edited:
You make a good point. I am not sure why the NEC and BS take different approaches here, and looking at the NEC table the ratio is greater than I thought on small circuits (i.e much smaller than the crossover point around #2). I would like to plug some numbers in and see how much impact it has but time doesn't permit. @marconi will be along presently, he often seems to have more patience for number crunching than I do!
 
Last edited by a moderator:
Obvious Question: is the software free?

Also, can you calculate short circuit current using this table and ohms law with the assumption of an infinite source?
 

Reply to Calculating Voltage Drop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am working on a RV Park and I have a question. I plan on installing 4/0 quadraplex AL URD cable to 10 pedestals on a 200 amp circuit and...
Replies
0
Views
204
Hi everyone. I am really puzzled by this, but I suppose there is an obvious answer / reason! Anyway, Table I1 in the OSG says the mΩ/m value for...
Replies
2
Views
678
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
887
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock