bit of reassurance on coding
I have 3 phase 3x150a (checked with supplier) incomer feeding meter in 50mm tails- 5omm tails to 3x blocks from meter
from each block tails to various isolators all not exceeding 1m in the same cupboard, the highest fused isolator at 60a being fed with 16mm and other various isolators around 32a -60a
anyway Im judging between c3 or c2 as the demand can't exceed 60a just after your thoughts
 
What are the blocks rated at?
Normal Henley blocks wouldn't be 150A I would think...
 
As long as the tails are suitably sized for each switched fuse and the service connector blocks are rated at 150A or more (which I'm guessing they are if 50mm fits in them) then there no issues with current rating.
 
What are the blocks rated at?
Normal Henley blocks wouldn't be 150A I would think...

Normally no, but also they normally don't accept 50mm conductors so it's likely that these are going to be rated at more than the usual 100A.
 
Peeps you are presuming that the tails haven’t been given a haircut!
It would not be the first time for me to find wiring given a trim to fit into a connection.
 
Peeps you are presuming that the tails haven’t been given a haircut!
It would not be the first time for me to find wiring given a trim to fit into a connection.

It wouldn't be the first time for many of us, but we can only assume the OP would have noticed that.
 
  • Like
Reactions: DPG
From the information supplied, I’m struggling to think of a reason why a code would be applicable.
Perhaps the OP could tell us why they think a code is warranted?
 
thanks for replies yes 200a blocks checked
the reason I was wanting to code was the fact that someone may replace a fuse in one of the iso for +80 and then we have an issue
which is quite possible as I found a fuse wire in a sub board had been replaced for a bit of 2.5
 
You can’t really code because someone might replace a fuse with a different size.
The same applies with boilers and extract fans.
 
  • Agree
Reactions: Andy78

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
commercial meter tails
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
Justin2211,
Last reply from
Justin2211,
Replies
14
Views
2,452

Advert