According to the on site guide,when polypipe incomer no main earth bond required as already pointed out,one of the first things i do when looking to upgrade to a new consumer unit is to check the sizing and connection of all earthing conductors,saves any problems later,anyway,one way of introducing earth potential might be an outside water supply in copper etc.mind you they say u dont need it on polypipe but on new builds i put it in just incase they change the regs in years to come and say its needed.
 
As already said, if it is a plastic pipe then no need to main earth bond, but you still need to make sure that the resistance is low between pipes and class II equipment in the bathroom (sorry I have forgot the formula) to rule out supplementary bonding.
 
Bond it. they can't fail you for overdoing it, but they can if the assessor thinks it should be done and it ain't
 
As already said, if it is a plastic pipe then no need to main earth bond, but you still need to make sure that the resistance is low between pipes and class II equipment in the bathroom (sorry I have forgot the formula) to rule out supplementary bonding.


touch voltage of 50V and current thru rcd of 30mA (0.03A) so R = V/I = 230/0.03 =1667ohms
if R is < 1667 Ω no supp bonding needed
 
Aside from the main topic of whether main bonding is needed or not

If you decide that it is not going to be installed
You must carry out supplementary bonding in the bathroom because you can not meet the conditions for ommision
It has to be a building with protective equipotential bonding to do so

There seems to be a lot of opinion saying not required,my own understanding is that a full cooper system would require the main bond ,whereas if the supply and major parts of the plumbing are plastic then omit
 
Again, i agree with Des.

However, if im doing a rewire, then ill always throw in a bond, even if not needed due to poly incommer.

Wasteful? ... Maybe.
 
Had a house that had no bond to water and a radial circuit with 4 sockets on it a cold water feed to a pump due to low pressure on the icoming main plugged into a socket on a radial plug a socket tester in all ok Zs the socket high readings , socket tester in reading unplug the pump earth fault the house was all plumbed in plastic but was finding a small earth through the water so there is still the potential from the water service be it only small its possible if its copper , but asringer has been said contact your trade body for advise,personally i would install the bond, always do
 
Last edited by a moderator:
IMO a main bond should be provided on the first available section of copper...even if the service is not introducing an earth potential at the time of the install conditions may change......CYA.
 
As already said, if it is a plastic pipe then no need to main earth bond, but you still need to make sure that the resistance is low between pipes and class II equipment in the bathroom (sorry I have forgot the formula) to rule out supplementary bonding.

Sorry , but do you mean Class I?
 
4.4 OSG is saying you do not have to bond if both supply and house pipework is plastic but if supply is plastic and house is copper then recommend you earth it in other words earth the bl+%6 pipework if metal because if you dont then Jobs Worth inspector who is probably reading forums like this will pull you up for not doing so and why would he do this ? because he can and he has the power to say sorry you fail and I am just doing my job and this is how I show my manager nothing gets past me.
What I would say is this environment suffers from the lack of definition and open season on interpitation but what I have learned is if you go up against the people who police our trade then human nature dictates that they dig in because they can.
 

Reply to CU Change - No main earthing on water main. Polypipe incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
780
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
862
I am due to carry out an electrical job in a third floor flat. Incoming supply is TN-S. Cannot locate a main earthing conductor inside the CU on...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock