Hi, I think I may have helped hold the gun in the shooting of my own foot…
Been combining TP dis boards into a single board, after a workshop extension. Quite a few 4 core 1.5mm SWAs feeding fixed equipment, like TP drills lathes and the like – all fed via 16A breakers on the old board.
Lots of the cables were just slung in purlins, that are no longer there due to the extension, so I had to extend them and move them onto a new Cable trays.
Just took a look at the regs re cable sizes and I see that in putting in nice new cable trays and fixing the cables to them, I have now introduced a grouping factor (to be fair it was already there so I think I have inherited this). The It value for 1.5mm SWA (4D4A) is 19A. Grouped, now moves this to around 24A…
How serious is this as an issue, considering its been in for over 20 years like this…
Options to put right I guess are, to reconfirm circuit Ibs (which i should have done to begin with) and reduce IN if I can. Failing that increase cable to size for the correct rating, 2.5 / 4mm.
Any ideas?
Cheers
John
Been combining TP dis boards into a single board, after a workshop extension. Quite a few 4 core 1.5mm SWAs feeding fixed equipment, like TP drills lathes and the like – all fed via 16A breakers on the old board.
Lots of the cables were just slung in purlins, that are no longer there due to the extension, so I had to extend them and move them onto a new Cable trays.
Just took a look at the regs re cable sizes and I see that in putting in nice new cable trays and fixing the cables to them, I have now introduced a grouping factor (to be fair it was already there so I think I have inherited this). The It value for 1.5mm SWA (4D4A) is 19A. Grouped, now moves this to around 24A…
How serious is this as an issue, considering its been in for over 20 years like this…
Options to put right I guess are, to reconfirm circuit Ibs (which i should have done to begin with) and reduce IN if I can. Failing that increase cable to size for the correct rating, 2.5 / 4mm.
Any ideas?
Cheers
John