I can't find any really up to date threads on whether we have to fit AFDD's.

I am specifically talking about in a domestic premise. I can see that 421.1.7 shows where an AFDD HAS to be fitted (i.e in one of the 4 bullet points), but then it says below ( the bullet points) it is 'recommended' that AFDD's are fitted in ALL premises for socket outlets.

The Napit Webinar (02/11/2022) kind of skips lightly over this point. At 11 mins and 25 seconds he says something along the lines of 'it is up to the designer whether to use the recommendation of using AFDD's'.

It clearly is not mandatory otherwise the reg would not state the 4 examples of where it actually is mandatory. So it is actually optional, but there isn't any criteria given to help you decide whether or not you should fit one.

Does anyone have any clarification on this?
 
You have answered your own question as such.
Yes, they are recommended but not compulsory. If, however, you are in a house where someone perhaps has a disability/mobility issues, you may think it prudent to fit AFDDs to help prevent the risk of fire.
It really comes down to you as the designer and the customer because they have to pay for it.
 
  • Like
Reactions: robd and oracle
You have answered your own question as such.
Yes, they are recommended but not compulsory. If, however, you are in a house where someone perhaps has a disability/mobility issues, you may think it prudent to fit AFDDs to help prevent the risk of fire.
It really comes down to you as the designer and the customer because they have to pay for it.
The bit I'm kind of getting at is the criteria for fitting AFDD's.

You have used some of your own judgement to decide that you 'may' fit an AFDD in a house where the occupier has a disability/mobility issue.

You haven't said you WILL fit one in the above scenario, just that you 'may'. So you've made a judgement in the first place that someone with a disability needs one, but not definitely.

What type of disability issue? What kind of mobility issue? Severity of disability etc. We'll need to have a bit of medical knowledge to make those decisions.

The point I'm getting at is there isn't any criteria. It's just a judgement call. It doesn't seem to be a judgement call that is based on any electrical knowledge. It is based on hundreds of other factors.... mobility, disability, what the house is made of, existing condition of house, age of wiring, does the house have rodents and many, many more.
 
  • Like
Reactions: suffolkspark
You're right. There is no exact criteria. Essentially it is up to you as the designer to decide if it is necessary in any given circumstance. This is just my take on it though. I may well have it wrong.
The BBB at it's vague best.
 
Yea its a bit crap, because if we go against the recommendation, and something goes wrong, where do we stand. Why did we not fit something recommended by the more knowledgeable iet?
 
  • Agree
Reactions: HappyHippyDad
They are mandatory on circuits containing socket-outlets in HRRBs (higher risk residential buildings). They are not mandatory generally in domestic premises. A recommendation is simply that - a recommendation. It does not compel you.
 
  • Like
Reactions: DPG
Who knows!!!!

Probably the worst wording in the whole of the regulations.

Basically AFDD is Recommended, so it is tempting to believe you don't have to.

However the regulations define recommended, as meaning that this is the option they advise in order to achieve the protection required (see page 18) (paraphrased to match this aspect).

So you don't HAVE to use AFDD to provide protection for arc faults, you could use something else. But ultimately you do need to do something to protect against arc faults. The regulations recommend AFDD as the tool to use.

The thing is there is nothing else!

I think they added "recommended" thinking about the traditional use of the word, unaware or forgetting that it had actually been qualified somewhat specifically in the regulations.

Bit of a mess in my opinion.
 
Try getting hold of them at the moment!
 
The bit I'm kind of getting at is the criteria for fitting AFDD's.

AFDDs are currently rare and very expensive, the IET know that they won't get fitted by a lot of jobbing electricians doing one-off jobs, rewires, CU changes etc. They also know that for those kind of jobs customers aren't going to accept the cost and will often choose the electrician who ignores the rule if they were to make them mandatory.

The only way the price is going to come down is by AFDDs becoming more commonly used and demand increasing.

By making it a recommendation they know that the people designing/specifying large scale domestic installation jobs, like whole new build estates, will specify AFDDs.
Housing associations, councils, listed buildings people will also start jumping on the band wagon and specify them.

This way the demand will increase and so drive the price down.

In the future we will see them become mandatory everywhere, but not until it is reasonably possible.

Now the cynic in me also wonders if making this a recommendation is also a way of dodging the blame if AFDDs do prove to be as troublesome and unreliable as some think they will be.
 
Adding any electronic circuitry is going to make the installation less reliable in terms of nuisance tripping and failure of the device itself.

Extract from some research into AFDDs:

If it is assumed that some amount of Electrically Initiated Fires (EIF) are initiated by arc-faults, there is still
significant doubt whether the introduction of AFDDs will effectively manage that risk. Empirical and
documentary evidence affirms this, for example, the tripping thresholds stated in the AFDD product standard are higher than the levels at which arc-faults could still cause ignition.

Any benefit brought by AFDDs is not sufficiently evidenced, the incidence rate of AFDD-detectible arc-faults is unknown. The primary disbenefit to AFDD technology is cost, which in a circumstance where AFDDs become mandated, may have the unintended consequence of delaying recommended improvement works.

An additional unintended consequence might be the distraction from more effective prevention of EIF, which principally would involve measures to reduce the general incidence of electrical faults through regular testing and inspection.
 
  • Winner
Reactions: Simon47
I live in a timber clad and old oak barn conversion. It has been fully rewired to a high standard. Because of multiple buildings, we have multiple CUs, all Hager. We recently decided to fit AFDDs to all areas where we have any kind of fire risk concern and had no difficulty getting them via our trade accounts. What is interesting is the resistance to using them which I think is largely driven by cost. We paid £102 each, plus fitting and testing and some other necessary changes due to CU space. This is not a trivial sum for AFDD multiples in domestic properties. I am a developer, not a qualified electrician, though I am familiar with the regs. If the regulatory authorities think AFDDs will materially reduce fire risk then having vague wording like "recommended" is ridiculous. Eventually insurance companies will drive this. I specify them in developments now. They make sense to me.
 
  • Like
Reactions: Simon47 and pc1966
Cost is one consideration, but their effectiveness in detecting different types of arc is another valid concern. In the US, the use of these devices has been controversial due to considerable issues with them -what I don't know is whether those issues are down to arc fault detection devices or widespread problems with fixed wiring and these devices functioning as intended.
 
Others have said most that needs to be said about this, but I guess for non-mandatory situations you need to consider how you might try, however vaguely, to quantify the risk elements that might justify fitting AFDD (or not):
  • Is the circuit likely to have equipment of questionable reliability attached? For example, some rental or public sockets would be riskier than a commercial setting with PAT checked stuff, or a newer home with new equipment in use.
  • Is the building construction one that is more likely to burn or have a high speed of fire propagation? So old wood buildings or conversions, or places where flammable material might be stored could be factors to apply.
  • In the event of a fire, are there unusually big consequences? So a building with folks of limited mobility and/or mental capacity to respond a factor in term of risk-to-life, a historic building or museum might be a factor in terms of loss of irreplaceable material, or high-rise where fire-fighting could be difficult to deploy, etc.
On the flip-side, there might be situations where AFDD are a poor technical fit and are not justified by the above, so places with power tools and similar in use where arcing is likely to trip them.

How you actually weigh up the above is not something I can answer! But if you have no specific reasons to say there is above-average risk, then you could argue that they are offering a negligible advantage and the cost of fitting would be better spent by the customer on linked fire alarms (if not already present) or fire extinguishers, etc.
 
I am sorry but the cynic in me observes the fact that the people making AFDD devices sit on the board recommending them. That alone makes me reticent. Then the cost. Most clients will baulk at the cost. On top of that there was a somewhat torrid thread from our partners over the pond re the matter of AFDD suggesting that we do not need them as with our voltage and the use of RCD we already have systems in place that will detect an arc fault and AFDD are superfluous. Essentially, I agree with that contention.
I could take the view that lets throw everything and the kitchec sink at "safety" and cover my derriere. As long as the client can afford it why should I think about these heady matters just comply and charge the customer.
Pragmatically it is not as simple as that. Most clients, domestic wise, will not buy it.
Bottom line; there is currently no neccesity to fit AFDD right now. But....as in the case of RCD, there will be. Whats not to like? We bring in a slight change to the regs, we can charge for a whole new set of OSG, BS7671 and bingo on the product! This will become invevitablly compulsory, at the moment it is not in average domestic wiring. If there is any ambiguity in the definitions that is JPEL's fault not mine.
 
On top of that there was a somewhat torrid thread from our partners over the pond re the matter of AFDD suggesting that we do not need them as with our voltage and the use of RCD we already have systems in place that will detect an arc fault and AFDD are superfluous. Essentially, I agree with that contention.
Another reason is our house wiring doesn't use aluminium cable (except for a tiny number of examples) that is far more likely to suffer arcing than copper wiring.
 
Ive just put a board full of afdds on a thatch re wire as im not on a price so thought even if it gives 1% extra safety im doing it, (im an ex fireman and they burn well 😅) but the rest of my jobs i wont, they do have Bluetooth though so you can communicate with them with your phone with the hager app 🤣
 
An architect friend of mine is just doing a large thatch extension on a job. He's specified AFDDs and I agree it makes a lot of sense with thatch. It's very difficult to get useful data on the cause of electrical fires. Anecdotal evidence seems to suggest that it is rarely faulty wiring in the UK (if done properly by skilled electricians to regs). Faulty appliances such as dodgy washing machines seem to get fingered quite a lot. These things generally are low priced and poor quality and end up in rentals and social housing. Arguably that is where protection is most needed and least likely to occur.
 
I can't find any really up to date threads on whether we have to fit AFDD's.

I am specifically talking about in a domestic premise. I can see that 421.1.7 shows where an AFDD HAS to be fitted (i.e in one of the 4 bullet points), but then it says below ( the bullet points) it is 'recommended' that AFDD's are fitted in ALL premises for socket outlets.

The Napit Webinar (02/11/2022) kind of skips lightly over this point. At 11 mins and 25 seconds he says something along the lines of 'it is up to the designer whether to use the recommendation of using AFDD's'.

It clearly is not mandatory otherwise the reg would not state the 4 examples of where it actually is mandatory. So it is actually optional, but there isn't any criteria given to help you decide whether or not you should fit one.

Does anyone have any clarification on this?
Your right there are certain situations where they shall be fitted, which seems quite clear. Anything other than this is a recommendation which means it does not need to be done
 
  • Like
Reactions: nicebutdim
Right up to the point when something disastrous happens that is determined wouldn't have happened if an AFDD had been fitted
As long as you have followed the regulations and don't decide yourself what constitutes as a recommendation then there is no come back. The regs aren't there to trick you. They may seem to contradict themselves sometimes but a recommendation is a recommendation. When it comes to AFDDs they state where you shall you them, and even define what they mean and the recommend where else they could be used. If you decide that your not sure then use them everywhere then you won't need to worry.
 
Ive just put a board full of afdds on a thatch re wire as im not on a price so thought even if it gives 1% extra safety im doing it, (im an ex fireman and they burn well 😅) but the rest of my jobs i wont, they do have Bluetooth though so you can communicate with them with your phone with the hager app 🤣
You will have to let us know if they give any problems. 😀
 
Recommended does not mean you have too,however i always plan a defence in case this is questioned at any time .mine would read : it does not state “shall” (unless it does) ,good workmanship ,following equipment manufacturers instructions , checking all screw fit joints and of course proper inspection and testing with all results as expected or calculated . You could probably go further than this with proper cable supports,safe zones rcbos. For lighting for instance a series arc current (with led lamps) will most likely never be reached .
 
Ive just put a board full of afdds on a thatch re wire as im not on a price so thought even if it gives 1% extra safety im doing it, (im an ex fireman and they burn well 😅) but the rest of my jobs i wont, they do have Bluetooth though so you can communicate with them with your phone with the hager app 🤣
That is a very good example of where AFDD would be a sensible choice even though nor mandated.

Also I suspect owners of thatched roof properties can probably afford it, if not then they can't afford to maintain the thatching!
 
  • Like
Reactions: freddo and mainline
Update from napit technical team relating to when you have to fit AFDD in domestic premises and it's view on the term 'recommended'...

"Thanks for watching the AFDD webinar, we are pleased you enjoyed it. The term recommended is not a new requirement for AFDDs, if you refer to the 2018 Edition of BS 7671 (blue copy) Reg 421.1.7 recommends AFDDs for all AC final circuits. Unfortunately, with so many different installations and different user types it can only be a decision made by the designer after considering all aspects."

Basically they're saying it's up to us if we fit them. In reality, hardly anyone will fit them at present due to the cost. If there is a fire due to electrical arcing and it goes to court, the IET will say 'well we recommended it." A disappointing reply to my thorough question (although I pinched the wording from @Julie 's professional sounding post 😀)

I think, as part of my quote I will recommend AFDD's to be fitted. I'll perhaps write a small amount about there use, and then leave the customer to make the decision.
 
Never fitted one and until they become common place at less than 1/2 the price I won't be fitting any
Neither will I Dusty, but the point being... If there is a fire due to arcing then it will be the electrician who is deemed to be at fault because the IET have covered themselves with the word 'recommended'. I will now continue this bottom covering exercise by also adding the word 'recommend' in my quote.

Then, in 2-5 years we can all fit them as standard when they come down in price.

Then, we can all talk about the latest addition to the rcbo/afdd, with something else added to it which costs a fortune etc etc 😄.
 
Wonder if an AFDD would of worked here 😀

F4F440D1-AEF4-4805-A858-40551E0309EA.jpeg
 
If it was a serial arc then no, low current arcs are not detected,in the USA maybe as there current will be twice ours for the same wattage
 
May have started with a serial arc, but there's enough carbon there to leak sufficient current to the cpc to trip a RCD.
Maybe not before catching the house on fire, though.
 
Ive got a EICR to do today that requires measuring the building height ( floors ) to see if it come under HRRB regs and needs AFD’s

They better hope its under 18m !! Otherwise its 5x new AFD and thats not cheap !
 
I live in a timber clad and old oak barn conversion. It has been fully rewired to a high standard. Because of multiple buildings, we have multiple CUs, all Hager. We recently decided to fit AFDDs to all areas where we have any kind of fire risk concern and had no difficulty getting them via our trade accounts. What is interesting is the resistance to using them which I think is largely driven by cost. We paid £102 each, plus fitting and testing and some other necessary changes due to CU space. This is not a trivial sum for AFDD multiples in domestic properties. I am a developer, not a qualified electrician, though I am familiar with the regs. If the regulatory authorities think AFDDs will materially reduce fire risk then having vague wording like "recommended" is ridiculous. Eventually insurance companies will drive this. I specify them in developments now. They make sense to me.
NOT HAGER my god anything but them....they dont even trip when they are nearly on fire
 
Ive got a EICR to do today that requires measuring the building height ( floors ) to see if it come under HRRB regs and needs AFD’s

They better hope its under 18m !! Otherwise its 5x new AFD and thats not cheap !

Not necessarily 5x new AFDDs, that would only be a C3 and so a recommendation, not a requirement.
 
  • Agree
Reactions: DPG and pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Do we have to fit AFDD's in domestic installations?
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
42
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Simon47,
Replies
42
Views
8,607

Advert