Hi all,

Currently quoting for a fairly extensive remodel of a kitchen diner, and I have a couple of things I'd appreciate a sanity check on.

1. Structural steel bonding - My brain is telling me based on what I've read and understood that I don't need to bond the new structural steels. They aren't in contact with the ground, but my heart is telling me that just seems wrong somehow. One of the beams is going to have it's cavity acting as trunking effectively since it's the path of least resistance from one side of the room to the other and so my thinking is, I should bond it to ensure a good earth path in fault conditions.

2. Sanity check on a cable size - New oven, 22.2A (max, no diversity factored in at all). 6mm can handle it, but obviously running a 20A breaker at that is not great long term, so 32A breaker required. Since 6mm can only handle 27A when in a ceiling with insulation (ref method I'm going to be encountering), my only choice is 10mm. Voltage drop is fine either way, it's just the potential overload situation. So 10mm is the correct choice as far as I'm concerned.

3. There is going to be some under cabinet lighting. To future proof, I am going to suggest that the supply for this (coming from a 6A lighting circuit) is exposed in the cupboards as 13A unswitched outlets since then the customer can change the lighting to their hearts content. My concern though is if they stick something other than lighting on it. 1.5mm is fine generally, and can handle 13A in the ceiling with insulation. So my brain is saying this is fine, but for some reason it just feels wrong. For that reason I was considering providing the supply by 5A round pin outlets, but that raises the issue of the 6A breaker. I have very limited experience of round pin outlets. 5A is obviously the continuous rating, try as I might, I can't find any information about overload characteristics, so I'm wondering what you guys think?

Whilst it's a fairly big job (by my standards so far), the rest of it is straight forward, it's just these three niggles I could do with a bit of feedback on.

Comments and thoughts welcome :)
 
There is a 150mm safety zone created at the angles of two faces of the wall no? Therefore it is within a safety zone where the window is, but that zone stops 150mm below the window sill... at least that's my take on it.
Because most people (except electricians) have no idea of safe zones I tend to try and limit the use to the most obvious locations where possible. Since the zone description is 150mm from the angle of two adjacent walls I do not think that this applies for a penetration through a wall such as a window frame.
You can also think that is someone is hacking out the window to change it they may well hit a cable; however a similar problem occurs with coving on the 150mm from the ceiling zone.
 
There is a 150mm safety zone created at the angles of two faces of the wall no? Therefore it is within a safety zone where the window is, but that zone stops 150mm below the window sill... at least that's my take on it.
Must admit, I'd never thought of a window opening as usable as a safe zone. Would you also regard a door opening in the same way?
 
I guess it's one of those issues that's open to interpretation. I'm planning on adding an outlet at the bottom of the wall just in case and I'm annotating plans for the customer showing where the cable runs are along with junction boxes. Aside from a blob of dot'n'dab, that cable's of the only one that causes me concern in terms of location wrt the zones.
 
Think the whole zone thing is a daft idea, only sparks know about it. Repaired loads of 'drilled into' cables directly above faceplates, nearly done it myself once :oops:

Incidentally, do plumbers have such zones?

Came across this doing kitchen refurb'. The gas pipe fed an unused gas outlet for kitchen cooker, which wasn't directly below it;

IMG_1537.JPG

The three holes were for the old wall unit brackets, luckily the drill bit somehow managed to miss the pipe.

Edit, the cut oblong hole I did, so we weren't attempt the same thing.
 
Last edited:
Think the whole zone thing is a daft idea, only sparks know about it.

I certainly agree with the above,it would not be so daft if the zone secret wasn't limited to the very people who install the cables and also the knowledge expanded,not only to include other trades, but rammed down the throats of the designers of kitchens,these seem to have no perception of the absolute chaos their efforts can cause
 
Think the whole zone thing is a daft idea, only sparks know about it.

I certainly agree with the above,it would not be so daft if the zone secret wasn't limited to the very people who install the cables and also the knowledge expanded,not only to include other trades, but rammed down the throats of the designers of kitchens,these seem to have no perception of the absolute chaos their efforts can cause

Gotta agree with that. Loads of time I go to quote for the kitchen electrics, and the designer has moved the electric cooker to the other side of the kitchen, and CU has no RCD for that circuit.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

SparkyChick

Broke Internet
Esteemed
Supporter
Joined
Location
South Wales
Website
http://www.sparkychick.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
SparkyChick

Thread Information

Title
Domestic remodel - Sanity check on a couple of things
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
46
Unsolved
--

Advert

Thread statistics

Created
SparkyChick,
Last reply from
Midwest,
Replies
46
Views
4,943

Advert

Back
Top