Guys, am doing a maisonette, the meter box is downstairs in the garage and the CU is approx 8 metres away so have pulled in some SWA as a sub-mains (25 mm2 3 core using one of the cores as the main earth). Have a CU that I can’t gland into, and the other end the SWA is going into the meter box. Realise that I need to bond the armoured as an exposed conductive part, any practical ideas as to how? Many thanks:confused:
 
Hi,
Is it a TT, TNS or TNCS system ?

Also, you will need some kind of double pole isolator from the incoming supply to your c/u ( as you now have set up a submains as you have mentioned ).

Sav
 
Also, you will need some kind of double pole isolator from the incoming supply to your c/u ( as you now have set up a submains as you have mentioned ).

Can I not use the self connect switch (100A DP) next to the meter for that?
 
Last edited:
Gland SWA into a metal switch fuse at supply end and earth box and armour there.
 
Can I not use the self connect switch (100A DP) next to the meter for that?

No as that is just an isolator and does not provide overcurrent protection for the sub main.
 
So,
25mm tails from your incoming mains supply, into your double pole Isolator (work out fuse rating ).
Make off your swa into isolator using gland kit and earth the armoured via banjo into earthing bar in isolator. You will also need an earth from the earthing bar to go into the MET.
If your c/unit is plastic, then you can still make a 25mm hole at the bottom and again using a gland kit, earth the armoured using a banjo.

Hope this is of some help,
Best regards,
Sav
 
Not all CU's will take a 25mm SWA gland as the covers go right over and back to the wall.

If installation methods allow, split con would have saved all the hassle :)
 
Possibly not that well thought through on my behalf, however tbf the CU is wall mounted on a stud wall with everything coming in from the back so not sure where I'd have got a gland in there... am a bit worried as to how much room I will be left at the meter end by the time siemans come and do their bit as to whether or not I'll get a metal DP switch fuse in there
 

Reply to Earthing armoured on a sub-mains in the Australia area at ElectriciansForums.net

Similar Threads

As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
881
I have a metal Hager sub CU, 10 way RCBO, installed in 2018 in an accessible attic space, this sub-CU being fed from another unit close to the...
Replies
11
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock