Hello,

I've recently had an EICR done on my 2 bed house which is a residential let. This house is about 25 years old built by Charles Church.

The EICR has not been issued due do C2's, there were no C1's
Email with C2s ratings for 1) Not all circuits RCD protected, 2) Bathroom light is a bare build not IP rated and 3) Hall pendant missing skirt cap.
I have no more detail at present ... just an email with bullets.
Just to reiterate I have some circuits with RCDs just not "all" circuits with RCDs!

I have challenged the email from the estate agent and received this response.

"As for the codes, any privately rented property nowdays requires rcd protection across each and every circuit to ensure safety to the tenants, failure of 30mA rcd protection on any circuits causes a C2 code when then the EICR fails as it cannot pass with any C2 codes present. (I'm currently having this problem at 90% of properties I'm conducting EICRs at) so unfortunately it is mandatory. 100% a code 2, it's different if it's in your own household then it's a code 3, but a rented accommodation it's a code 2 as all circuits have to be rcd protect for the safety of the tenants.

I will break the quotation down further for you with a full quotation typed up thoroughly shortly."

So the question and help required is
QUESTION: Is it a REQUIREMENT to have RCDs on "all" circuits to avoid a C2 rating? My position after limited research is no it is not a C2
HELP REQUIRED: How do I proceed? The property manager Romans Estate Agents in Berkshire is the individual supporting the Electricians position!

Report yet to be issued/released by the Estate Agent and or Electrician
 
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members

Risteard

-
Arms
Esteemed
As it is a Report it should be issued irrespective of the fact that it may state that the electrical installation is "Unsatisfactory". To put it into context, probably 95% of the inspections I carry out result in "Unsatisfactory" being recorded. The important thing is that you have remedial works carried out as necessary (and certified as appropriate).

Lack of 30mA RCD additional protection is likely to attract different classifications/codes against it in the observations depending on the reason for the requirement. As an example an electric shower without 30mA RCD protection may not be classified the same way as concealed cables buried in the wall at a depth of less than 50mm and not otherwise mechanically protected e.g. with Earthed steel conduit.

It is also incorrect to state that all circuits in domestic dwellings require 30mA RCD protection. Very often that will be the most economic way of installing, but there is no blanket requirement for 30mA RCD protection on all domestic circuits.
 

GBDamo

-
Supporter
As always the introduction of new legislation has resulted in chaos and chancers.

My take is that all rental properties have to be tested to the 18th edition.

All editions of the regulation have a statement to the effect that they should not be retrospectively applied.

So, unless your property was built to the 18th then it need not fully comply with the 18th. It must however full comply with the edition in use when the property was built/refurbished.

There is as always nuance and some situations will receive a C2 even when not in contravention of the regulations in force at the time.

In brief, some circuits need not be RCD protected. Socket and all bathroom circuits should. General lighting the odd fused spur radial need not.

Ideally, budget allowing, there is a good safety argument for RCD protection of all domestic circuits.
 

Matthewd29

-
Arms
Esteemed
Hello,

I've recently had an EICR done on my 2 bed house which is a residential let. This house is about 25 years old built by Charles Church.

The EICR has not been issued due do C2's, there were no C1's
Email with C2s ratings for 1) Not all circuits RCD protected, 2) Bathroom light is a bare build not IP rated and 3) Hall pendant missing skirt cap.
I have no more detail at present ... just an email with bullets.
Just to reiterate I have some circuits with RCDs just not "all" circuits with RCDs!

I have challenged the email from the estate agent and received this response.

"As for the codes, any privately rented property nowdays requires rcd protection across each and every circuit to ensure safety to the tenants, failure of 30mA rcd protection on any circuits causes a C2 code when then the EICR fails as it cannot pass with any C2 codes present. (I'm currently having this problem at 90% of properties I'm conducting EICRs at) so unfortunately it is mandatory. 100% a code 2, it's different if it's in your own household then it's a code 3, but a rented accommodation it's a code 2 as all circuits have to be rcd protect for the safety of the tenants.

I will break the quotation down further for you with a full quotation typed up thoroughly shortly."

So the question and help required is
QUESTION: Is it a REQUIREMENT to have RCDs on "all" circuits to avoid a C2 rating? My position after limited research is no it is not a C2
HELP REQUIRED: How do I proceed? The property manager Romans Estate Agents in Berkshire is the individual supporting the Electricians position!

Report yet to be issued/released by the Estate Agent and or Electrician
According to NAPIT, a C2 code is required in the circuits not protected by RCD situation, so although I personally would code it C3, there is a case for supporting the C2 there. I also agree with the statement that you should be doing everything possible to ensure the safety of your tenants, and realistically, upgrading all circuits to have all RCD protection is a step in that direction.
 

TJ Anderson

-
Mentor
Arms
Esteemed
According to NAPIT, a C2 code is required in the circuits not protected by RCD situation, so although I personally would code it C3, there is a case for supporting the C2 there. I also agree with the statement that you should be doing everything possible to ensure the safety of your tenants, and realistically, upgrading all circuits to have all RCD protection is a step in that direction.
A experienced inspector has to be able to apply their discretion when applying codes and also be aware of previous editions of the wiring regulations. Something being "Unsafe" and something that is "Not unsafe but could be made safer" are two different things. An EICR should not be used to up sell improvement works beyond recommendations to rectify unsafe situations.
 

ChrisElectrical88

-
Mentor
Arms
Esteemed
Get the report off her and stick it up here and you will get a better input. They legally have to give you the very even if unsatisfactory. Not all bathroom lights need to be a certain IP rating and a pendent missing a skirt is a C3 for me.
 

littlespark

-
Arms
Esteemed
As far as the electrician doing the report is concerned there should be no difference in coding between an owned property and one to be rented.

I’m sure there’s another thread on here mentioning that the new rules for all rented to have an EICR is worded wrong.

What happens in a few years when the 19th comes out?
 

Matthewd29

-
Arms
Esteemed
A experienced inspector has to be able to apply their discretion when applying codes and also be aware of previous editions of the wiring regulations. Something being "Unsafe" and something that is "Not unsafe but could be made safer" are two different things. An EICR should not be used to up sell improvement works beyond recommendations to rectify unsafe situations.
I am fully aware of that. I am not a member of NAPIT either but they code it as a C2. Merely pointing that out.
 

James

-
Mentor
Arms
Supporter
Esteemed
In my opinion, the regs have always been taken as correct at date of installation.
If something is deemed safe and up to standard when installed, I don’t like the presumption that it is unsafe when new regs are published.
I am sure there is a comment in the regs book that says pretty much the same thing but I am not going to look for it tonight.

Remember, if they did this with mot tests, there would not be a single classic car allowed on the road.
Are we saying that all classic cars are dangerous?
 
  • Thread Starter Thread Starter
  • #12
All,

I absolutely agree safety first!
Cost is not the issue
I want to understand if "not have all circuits RCD protected" is an automatic C2 rating
- Page 12 of the Best Practice Guide attached - implies to me no this is not a C2.
I am on here for guidance from experts. I am NOT an electrician. I would/ do appreciate your response and guidance.
 

Attachments

Best Practice Guides are not required documents to have or follow similarly, you also have the NAPIT guide often giving different advise. It is up to the individual how they Code things usually through knowledge and experience although most often this is not the case.
 

happyhippydad

-
Arms
Esteemed
All,

I absolutely agree safety first!
Cost is not the issue
I want to understand if "not have all circuits RCD protected" is an automatic C2 rating
- Page 12 of the Best Practice Guide attached - implies to me no this is not a C2.
I am on here for guidance from experts. I am NOT an electrician. I would/ do appreciate your response and guidance.
It is not an automatic C2, however it could well be a C2. Lots of landlords are starting to ask the same question and I think we need to focus on the fact that an RCD is a life saver.
If the electrician has given it a C2 and the estate agent is agreeing with the electrician then I think it's best to get the work carried out.
I always think that not having an RCD is like driving around in a car without a seatbelt on. You're fine until you have a crash.
 

telectrix

-
Mentor
Arms
Esteemed
I always think that not having an RCD is like driving around in a car without a seatbelt on. You're fine until you have a crash.

i would more liken it to having a seatbelt but not an airbag. similar to having ADS but no RCD.
 

davesparks

-
Mentor
Arms
Esteemed
If something is deemed safe and up to standard when installed, I don’t like the presumption that it is unsafe when new regs are published.
I am sure there is a comment in the regs book that says pretty much the same thing but I am not going to look for it tonight.
There is an often misunderstood statement in the regulations that compliance with a previous edition does not necessarily mean something is dangerous, potentially dangerous or in need of improvement.

This does not say that 'if it complied when it is installed then it is ok'
Post automatically merged:

Hello,

I've recently had an EICR done on my 2 bed house which is a residential let. This house is about 25 years old built by Charles Church.

The EICR has not been issued due do C2's, there were no C1's
Email with C2s ratings for 1) Not all circuits RCD protected, 2) Bathroom light is a bare build not IP rated and 3) Hall pendant missing skirt cap.
I have no more detail at present ... just an email with bullets.
Just to reiterate I have some circuits with RCDs just not "all" circuits with RCDs!

I have challenged the email from the estate agent and received this response.

"As for the codes, any privately rented property nowdays requires rcd protection across each and every circuit to ensure safety to the tenants, failure of 30mA rcd protection on any circuits causes a C2 code when then the EICR fails as it cannot pass with any C2 codes present. (I'm currently having this problem at 90% of properties I'm conducting EICRs at) so unfortunately it is mandatory. 100% a code 2, it's different if it's in your own household then it's a code 3, but a rented accommodation it's a code 2 as all circuits have to be rcd protect for the safety of the tenants.

I will break the quotation down further for you with a full quotation typed up thoroughly shortly."

So the question and help required is
QUESTION: Is it a REQUIREMENT to have RCDs on "all" circuits to avoid a C2 rating? My position after limited research is no it is not a C2
HELP REQUIRED: How do I proceed? The property manager Romans Estate Agents in Berkshire is the individual supporting the Electricians position!

Report yet to be issued/released by the Estate Agent and or Electrician
What a load of bull-poo!

The regulations are the same for all installations, it doesn't matter whether it is rented or not.
There are a number of reasons for installing RCD protection on circuits, depending on the exact situation a lack of RCD protection can be either a C2 or C3 item.

An EICR is not a certificate, it is a report.

The job you have employed them to do is carry out a report, if they have refused to provide you with the report then don't pay them and get another electrician to do it.
They have no right, or reason, to withhold the report based on the outcome of the report.

The overall assessment of an installation cannot be 'fail' it can only be 'satisfactory' or 'unsatisfactory'
 
Last edited:
As far as the electrician doing the report is concerned there should be no difference in coding between an owned property and one to be rented.

I’m sure there’s another thread on here mentioning that the new rules for all rented to have an EICR is worded wrong.

What happens in a few years when the 19th comes out?
Absolutely, littlespark, 1 day the 18th finishes, the next day the 19th starts. What happens? rewire everything?
Post automatically merged:

There is an often misunderstood statement in the regulations that compliance with a previous edition does not necessarily mean something is dangerous, potentially dangerous or in need of improvement.

This does not say that 'if it complied when it is installed then it is ok'
Post automatically merged:



What a load of bull-poo!

The regulations are the same for all installations, it doesn't matter whether it is rented or not.
There are a number of reasons for installing RCD protection on circuits, depending on the exact situation a lack of RCD protection can be either a C2 or C3 item.

An EICR is not a certificate, it is a report.

The job you have employed them to do is carry out a report, if they have refused to provide you with the report then don't pay them and get another electrician to do it.
They have no right, or reason, to withhold the report based on the outcome of the report.

The overall assessment of an installation cannot be 'fail' it can only be 'satisfactory' or 'unsatisfactory'
Eicr is a report, Well I think that's what the "R" is for!
 
  • Thread Starter Thread Starter
  • #20
All,

attached here is the EICR report .. to me it does not contain a lot of detail
Your opinions please.

How much detail in a typical report should I expect?
What is the rationale for C2s ratings ? Are they justified?
 
Last edited by a moderator:

Risteard

-
Arms
Esteemed
It's a very poorly compiled report to be fair.

You should redact names and addresses from it though, including those of the company responsible.

There is no requirement for 30mA RCD protection of all circuits. Although in practice this may well be needed on all circuits, it will actually be for a number of different reasons. These reasons should have been given rather than some incorrect statement.

There's no such thing as an "Amendment Type 3" board - but presumably he is referring to one made of non-combustible material or housed in a cabinet made from non-combustible material.

Likewise the bathroom luminaire may well have an IP rating, but presumably the issue is that it is an inadequate IP rating.

Lots and lots of boxes ticked in the Schedule of Inspections. I am doubtful that all of those things were checked and that all of them were compliant.
 

Strima

-
Arms
Esteemed
The lack of RCD protection for some circuits would normally attract a C3 as the sockets have RCD protection, caveat that all cables are run in zones etc.

Without seeing the other C2 items it's hard to say but I would err on the side of caution and agree with the inspector.
 
All,

attached here is the EICR report .. to me it does not contain a lot of detail
Your opinions please.

How much detail in a typical report should I expect?
What is the rationale for C2s ratings ? Are they justified?
I have deleted the report. Can you resubmit it so it does not show the contractors details and your address.
 
The lack of RCD protection for some circuits would normally attract a C3 as the sockets have RCD protection, caveat that all cables are run in zones etc.

Without seeing the other C2 items it's hard to say but I would err on the side of caution and agree with the inspector.
I have deleted the report. Can you resubmit it so it does not show the contractors details and your address.
All,

attached here is the EICR report .. to me it does not contain a lot of detail
Your opinions please.

How much detail in a typical report should I expect?
What is the rationale for C2s ratings ? Are they justified?
I the wiring was done before the 18th ed the worst would be C3, if that.
Unless you have bare wires etc sticking out then you would advise immediate attention, so no C1/2 anyway.
 

davesparks

-
Mentor
Arms
Esteemed
I the wiring was done before the 18th ed the worst would be C3, if that.
Unless you have bare wires etc sticking out then you would advise immediate attention, so no C1/2 anyway.
Coding does not change based on when something was installed, the inspection is carried out to the current edition of BS7671 and all items coded in accordance with the current edition.
 

Ian1981

-
Mentor
Arms
Esteemed
The aspects to be covered in an EICR include
Identification of non-compliances with the current edition of BS 7671, or installation defects, which may give rise to danger.

Must we go through this every time regarding eicr’s?
It is only logical that they are inspected against the current wiring regulations.
We all acknowledge the HSE foreword about how older installations are not necessarily unsafe etc etc, we cannot dig into the archives of wiring regulations based on when an installation was first put into service as safety has well and truly evolved.
 

davesparks

-
Mentor
Arms
Esteemed
Incorrect. as per front of book.
Front of what book?

It is made very clear in BS7671 that EICRs are carried out to the current edition and any non-compliance which has a safety implication should be coded accordingly. You are probably falling into the common trap of misreading the note that points out that compliance with a previous edition does not necessarily mean something is unsafe.
The key point about this is 'not necessarily' meaning it may or may not be unsafe, but non compliance with previous editions on its own is not grounds for something being unsafe.
Fused neutrals and red and black conductors comply with previous editions, one is safe and not coded, one is unsafe an coded.
 

Simon47

-
Arms
Esteemed
My experience with agents is that they tend to take what "the exoerts" tell them as gospel. I've had a number of communications that I've been able to tear apart - the sort of misinformation we've come to expect from the scams, filtered via an agent who doesn't know any better.
 
I don't have a copy of the Napit document to refer to, but my Youtube watching of late seems to be showing up some discrepancies between them and the ESF Best Practise guide, which is hardly reassuring to those of us still trying to find our way through the maze.

Personally, I'd say a reasonable attitude might be that a socket that is likely to be used for external use and is not RCD protected might well be a C2 (though replacing that socket with an RCD socket might resolve the issue), while a socket for a fridge in a 2nd floor flat (with suitable Zs and all other things being equal) might well be a C3.

Neither case is inherently "unsafe" though, so we are left to make judgements about what is an acceptable level of minimum safety, in the same way that 70s cars can still pass an MOT, without many of the safety features of 90s cars.

It seems rather like the powers that be are trying to be too prescriptive on one hand (with ANY C2 requiring an unsatisfactory rating, for example), while refusing to be clear or consistent in guidance, which is itself published separately and not necessarily binding on the standards we are all supposed to be following.

In other words, it's all a complete dog's breakfast as usual!
 

Simon47

-
Arms
Esteemed
Personally I think government are OK on this - you inspect & test to current regs*, and if there are C1 or C2 defects then the installation is dangerous and needs rectification. I lay the blame for the confusion at the door of the scams who have a vested interest in drumming up work for their members. I note that a lot of the discussion here relates to guidance from the scams - and specifically guidance suggesting defects be rated more seriously that some here think is warranted.

* Well, it would be if that's what the regs actually said.
 
I would say the whole problem is the EICR was never intended to be used to show if a property can be rented out, if to fit a new socket I will need to have a new consumer unit fitted, I need to know. I need to know what needs to be done to comply with current edition, so yes it is done to current edition.

There is a problem in I don't have a copy of the 14th Edition so I could not say if the property complied with it or not. This is from 17th Edition don't have 18th to hand.
BS 7671:2008 said:
BS 7671:2008 Requirements for Electrical Installations was issued on 1st January 2008 and is intended to come into effect on 1st July 2008. Installations designed after 30st June 2008 are to comply with BS 7671:2008.
Note the word "designed" so that quote says it does comply with 17th Edition if designed before 30st June 2008 and complied with edition current at the time.

C1, C2, C3 do not say does not comply with regulations, it says how dangerous it is, there was a 4 which said complies with previous edition, but that was scrapped. So ' Danger present. Risk of injury. Immediate remedial action required.' is the same what ever edition one is using. The same with 'Potentially dangerous - urgent remedial action required.' if it is potentially dangerous then that can't change depending on which edition. 'Improvement recommended.' however will depend on the edition used.

So the big question what makes some thing which was not potentially dangerous in 1992 when BS 7671 first came out, potentially dangerous today? The answer must be the equipment used today which was no available in 1992, so what we are looking at is the switched mode power supply, in 1992 we would transform voltage then regulate there were very few items which rectified mains, so the only change that I can see is the types of RCD used to protect with a TT supply. So I can see a good reason to issue a C2 when the RCD used on a TT supply is type AC. That is about the only thing which in 1992 was safe but in 2018 is not safe.

Can anyone think of anything else which is not safe today but was safe in 1992?

C2 does not mean does not comply with BS 7671:2018 it means potentially dangerous, and over the years the electrical characteristics of properties change, be it the water pipes changed to plastic, or the switch plates changed to metal, or even the supply voltage dropped from 250 to 230.

If I as an electrician but not a member of any scheme do any electrical work I need to issue a minor works or installation certificate, and if any of that work is on the list of notifiable work I need to inform and pay the LABC fee before I start, which is little more than a tax, the law has changed slightly in now in England I need to hold a level 3 or higher qualification, in Scotland seem to remember I must have attended a course in last 5 years, but in essence since I have passed my C&G 2391 I can if I got some professional indemnity insurance start doing EICR's which are legal. I can't issue a compliance certificate or a completion certificate, but I can make a report.

It seems SSE have an insurance, which for under £70 a year covers the house holder for any repairs to the electrical installation and there is a full report made before they take on the property and a yearly check done. Read about it on another forum, and the home owner was adamant his house was OK as nothing had been reported wrong, he has a TT system with a 100 mA RCD with no type marked on it. We were trying to tell him he needed a 30 mA RCD before fitting a new 9.5 kW shower, and the Wylex fuse board although the fuses had been replaced with MCB's was also past its use by date.

So most electricians do not want to end up in court, so we play safe, at least I do, and as far as an EICR goes that means following the electrical safety councils best practice guide even if I don't agree with it, I want to if I have to stand up in court to say I followed the recommendations. And to be frank I have all RCBO protection in my house, so to say to some one else you don't need it does not some how ring true, I made a mistake and thought I was fitting type B as that is what is said on the boxes, seems fitted type AC, so I have ordered 2 type A to replace those feeding the sockets.

So if you go into a property with those silly power line units fitted on a TT supply, do you give it a C2 unless fitted with type F RCD? If not why not?
 
Best Practice Guide 4 issue 5 said:
It should be borne in mind that, as stated in the introduction to BS 7671, existing installations that have been constructed in accordance with earlier editions of the Standard may not comply with the current edition in every respect, but this does not necessarily mean that they are unsafe for continued use or require upgrading
Best Practice Guide 4 issue 5 said:
Consumer units having rewirable fuses can continue to provide satisfactory service (cover removed for illustrative purposes)
Where some thing has been changed for example the earthing arrangement in a bathroom to a latter edition clearly it all needs to be to same edition, so it may NEED RCD protection.

The biggest problem I see where RCD's have been added is where when on fails to keep essential supplies i.e. freezer only option is to run cables up/down stairs, the risk of tripping over cables on the stairs likely exceeds the risk from shock not having a RCD.
 

Simon47

-
Arms
Esteemed
What has changed is both the perception of, and attitude to, risk. At one time, it was considered "normal" to have a bayonet plug on appliances and plug them into a light socket with no earth - while the risks from doing that have not changed (if anything they've reduced with things like double insulated appliances), our attitude to the risk of doing that have changed and we no longer consider it "safe".
 
The aspects to be covered in an EICR include
Identification of non-compliances with the current edition of BS 7671, or installation defects, which may give rise to danger.

Must we go through this every time regarding eicr’s?
It is only logical that they are inspected against the current wiring regulations.
We all acknowledge the HSE foreword about how older installations are not necessarily unsafe etc etc, we cannot dig into the archives of wiring regulations based on when an installation was first put into service as safety has well and truly evolved.
Thats your opinion,
Front of what book?

It is made very clear in BS7671 that EICRs are carried out to the current edition and any non-compliance which has a safety implication should be coded accordingly. You are probably falling into the common trap of misreading the note that points out that compliance with a previous edition does not necessarily mean something is unsafe.
The key point about this is 'not necessarily' meaning it may or may not be unsafe, but non compliance with previous editions on its own is not grounds for something being unsafe.
Fused neutrals and red and black conductors comply with previous editions, one is safe and not coded, one is unsafe an coded.
Playing with words, (again) lets say you have a water main earth, .3ohms. perfectly alright.
 