It's a very poorly compiled report to be fair.
You should redact names and addresses from it though, including those of the company responsible.
There is no requirement for 30mA RCD protection of all circuits. Although in practice this may well be needed on all circuits, it will actually be for a number of different reasons. These reasons should have been given rather than some incorrect statement.
There's no such thing as an "Amendment Type 3" board - but presumably he is referring to one made of non-combustible material or housed in a cabinet made from non-combustible material.
Likewise the bathroom luminaire may well have an IP rating, but presumably the issue is that it is an inadequate IP rating.
Lots and lots of boxes ticked in the Schedule of Inspections. I am doubtful that all of those things were checked and that all of them were compliant.