Yes, I believe the let out clause for installations which complied at the time of their design/construction would not apply to an installation which has never complied.Spin, you said in a previous post:
EICR- Are Rcd's necessary ? - https://www.electriciansforums.co.uk/threads/eicr-are-rcds-necessary.108681/
""The socket may well be used for the mower.
However the mower may have an RCD plug, or may be used with a plug in RCD adapter.
The socket (unless it is intended for a specific item of equipment) fails to comply with current Regulations, as it has no RCD protection. To then make a further observation based on the fact that it fails to comply with something that is no longer a requirement of the Regulations, would mean that you are not conducting the inspection, in accordance with the requirements of BS7671.
If it is the case, that at the time of design/construction of the installation, the requirement to provide RCD protection for socket-outlets which could reasonably be expected to supply portable equipment outdoors was in force, then you have an installation which has never complied with the requirements of BS7671.
As such the requirement which allows for installations which complied at the time of their design/construction to not be deemed unsafe does not apply.
This would mean that a code C2 would be applicable for all general use sockets, cables concealed in walls, circuits of locations containing baths or showers, etc.""
However, I would not be making an observation and applying a code about a non-compliance with a 16th edition Regulation that is no longer in use.