Discuss Fault Finding - Ring : Techniques? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Currently have an unknown fault on a ring circuit on a job i've been on, not had time to look as it was end of the day, wanting to know everyones techniques in finding faults on a ring in a house, as how the house is wired isnt going to be straight forward etc... your comments please
Unplug everything on the circuit.
Disconnect any neon fuse spurs / sensitive fixed appliances
Complete an IR test on circuit - if circuit ok - find faulty appliance.
If fault still on circuit - split circuit in the middle and IR test each leg.
Keep splitting the circuit on the leg where the fault remains untill the fault is found.
Repair / Replace / sorted
Warren
A TDR can be a helpful instrument in finding where the fault is, distance wise. If you have a half-decent idea of how the circuit is likely run, the TDR reading will give you a better idea of the distance at which you should begin to "divide and conquer".
mdshunk
I think most contractors don't know what a TDR is let alone know how to use one.:eek:
Warren
Dumb question and will prob kick my self once you say, but how do i find the middle of the ring ?
You can find the approx middle of the cable run by cross connecting the lives and cpcs and finding the highest r1 r2 reading but this may not be where the middle of the outlet quantities are
The best way I find is split the ring at the consumer unit and a hopefull central socket energise the clear legs and check which outlets are now live
and go from there
and go from there
You should be glad I'm not your boss as if I caught you doing the later you would be looking for a new job, a dangerous practice if I ever heard one. :eek:
You have an accident doing that and the HSE will be over you like the plague:eek:.
There is no easy way or answer.
All you can do is assertain which sockets are on the ring and and work out how you would wire it yourself. Then hope the origional electrician run it the same.
Good luck.
:eek:.
When a fault is cleared
Even if what was once a ring main now becomes a radial
Connecting that radial to an appropriate sized MCb and energising that circuit to ascertain the supplied outlets is standard SAFE practise
Where in your comment does the DANGEROUS PRACTISE reference apply to
If I were your boss I would ask where comments that you have given are contradictory to safety or regulations
If you had a lighting radial with a damaged cable during a fault finding excersise
If the replacement of that cable at that time was unable to be carried out
Would you not clear the faulty section of that radial in order to re-supply some of the lighting of the customer
The advise given is no different
My SAFE working advise will stand
A TDR meter would be ideal as the LCD screen would not only show where the fault is in terms of distance, but would also show how many joints existed in the circuit (a socket connection would be considered a joint) The TDR meter would also indicate if the fault was high or low resistance.
TDR meters are used extensivly is the communications industry and they are not cheap.
Reply to Fault Finding - Ring : Techniques? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...