Hi everyone was looking for some advice on a job that I looked at last night. The house has a new boiler being installed which needs a supply to it. There is an existing cooker switch wired in 6mm on a 30A fuse going to a single socket which the electric oven is plugged into. There is also a switched fused spur directly adjacent to the cooker switch wired in 2.5mm which used to supply an extractor fan. Is it ok to connect the new boiler to this fused spur or is the cooker required to be on its own separate circuit? There is also no RCD protection on the existing old Wylex board which uses bs1361 fuses. Thanks in advance!
 
can't see a problem here. the FCU is already energised i assume, so you are not making any alterations to the fixed wiring. therefore the lack of RCD is irrelevant. i'd certainly consider upgrading the CU though.
 
is the boiler going next to the fused spur? if your planning on burying any cable then you need to change it to an rcd spur unless the cable is otherwise protected.
 
good call. though why should manufacturers specify RCD when nothing in BS7671 calls for one?
 
Thanks for all the prompt replies I will check the manufacturers instructions later and also advise on upgrading the cu.

If the instructions are from a European/Scandinavian country manufacturer, (and most are these day's) then you can take most of the requirments with a pinch of salt!! Comply with BS7671 and you can't go far wrong....
 

Reply to Fused spur wired off cooker switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Wiring cooker hood into a switched fuse spur with a 13amp fuse in the spur. The cooker hood is 3amp. Should I swap out the 13amp fuse in the spur...
Replies
2
Views
354
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
783
Hi So converting a 6mm cooker connection point into a 13a unswitched fuse spur with the load being a 2.5mm pre wired cable from a oven . is this...
Replies
2
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
676
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock