chiplard

Am i allowed to install a radial circuit that supplies 1 single and 1 double socket in a garage with 1.5mm cable?

It is unsheathed cable in plastic conduit (ref method B). From the BRB this has a Current Carrying Capacity of 17A. It is on a 16A MCB and the load it supplies will be a freezer and maybe small power tools.

Discriminataion has been achieved but is this allowed?

Thanks
 
If the CCC of the cable is 17A (as you say) and it is protected by a 16A breaker, then I don't see a reason why not.!

I would however use 2.5mm cable myself.
 
Is there a particular reason why you are planning on using 1.5mm?
 
Not already installed but i have plenty of 1.5mm left from doing the lighting circuit. If it has to be 2.5mm ( to conform with the BRB and the inspector) then i will buy some 2.5mm.
 
Well if it were myself I would either try the circuit on a 10amp, with the expectation that it will trip now and then. Or more ideally use 2.5mm. ;)
 
Not sure where you would stand on this.....1.5mm is permitted to supply sockets on a ring or radial fused at 32/20 when subfused at a max of 13a via an FCU.....the arrangement you propose would not come under these standard circuit arrangements. Even though 1.5mm would appear to comply fused at 16a ,I would either run it through an FCU if you really want to use 1.5mm or do it properly in 2.5mm.
 
Thanks everyone. I will go for the 2.5mm option cos as wirepuller has said the BRB does say you need a 13A FCU to use 1.5mm ( didn't see that before !! )

Thanks again. :)
 
Thanks everyone. I will go for the 2.5mm option cos as wirepuller has said the BRB does say you need a 13A FCU to use 1.5mm ( didn't see that before !! )

Thanks again. :)

That would be with a CU fuse of 20 or 32a though....a 16a is a bit of a grey area, you are right to go with 2.5mm IMHO.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Garage Radial on 16a MCB
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
chiplard,
Last reply from
Deleted member 9648,
Replies
9
Views
7,721

Advert