Discuss Gas & Water bonded to 1 x 10mm cable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
1 x 10mm cable to both gas and water is absolutely fine as long as it is continuous.
Continuous as in A to B, not one complete piece of cable . A well made interconnection between the two bonds is no more at risk than any other high integrity joint.
regulation number please if you can
You do realise Pete that @westward10 will ask you for a reg number showing that it needs to be continuous :). I am desperately trying to find it! However, knowing his experience and knowledge level I fear there is not one :mad:
There is no reg as far as I can remember stating it must be continuous throughout its run.
You do realise Pete that Westward will ask you for a reg number showing that it needs to be continuous :). I am desperately trying to find it! However, knowing his experience and knowledge level I fear there is not one :mad:
There isn’t one....I believe it’s written in one of the guidance note books but obviously it’s only guidance. Its obviously considered best practice Incase a clamp is taken off by a wet pants etc but from a regs point of view it’s perfectly acceptable.
There is actually no Regulation in BS7671 stating it must be continuous so you can use a single conductor for both services continuous or not.
He's right Pete Q & A of the Day – What regulation for bonding adjacent gas and water supplies? - https://www.voltimum.co.uk/articles/q-day-what-regulation-bonding :(
He's like Davesparks, hardly ever wrong, but we'll get them one day!! I've only ever managed to prove Davesparks wrong once and that was on a technicality:D
Think about it Pete if you had a distribution circuit supplying an out building that had extraneous conductive parts. The earthing conductor in the distribution cable is of adequate size to be used as a bonding conductor as well as functioning as a CPC. This is then connected to the earth marshaling terminal at the far end and from this EMT, bonding conductors were run to water and structural steel separately, they would still be using the same single conductor from the EMT to the MET.....There really is no difference in using a bonding conductor from the MET to both gas and water.
Thanks guys for your knowledgeable replies regarding the bonding.
My second question; I have a situation where the gas and water enter a maisonette at the front door, the gas meter is on the first floor some 4 meters away from the point of entry. My question is; do I provide the 10mm bonding within 600mm of gas entry point or at the customer side of the gas meter?:(
Advise would be much appreciated
Reply to Gas & Water bonded to 1 x 10mm cable? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...