The speed governors were checked on all 3 engines at a very recent over haul. The mech fitters stripped the engines down to thier underpants and rebuilt them. The engines are now as good as they were when first bought. (so they tell us).
The fitters knew we were having what we first thought of as frequency problems so they (the governors) were set for a electricial load of 30A, the frequency matched to suit. (50hz at 230V, 30A load). The engines are normally set for 51Hz as this falls away at load, as does the Volts.
To answer your Question E54, the engines are controlled normally from a photocell, via a PLC, so that when the Main Light is called for, 1 of the engines start. This would supply the light and other navagational aids. (Its a lighthouse by the way).If this engine were to fail for any reason the control cabinets would detect a loss of power and start engine 2. Likewise, if this engine were to fail, engine 3 would start. When people are staying at the lighthouse for maintenance works, 2 engines can be run, 1 to supply the Light (called the A load), the other to supply the dwellings (called the B load). Loads can be split form a distribution control cabinet.
Under normal operating conditions when no one is at the station the load would be around 25A. 5A for the light, (1000W) 20A for a storage heater and battery chargers. The engines dont like working without a load so we install ballast loads (storage heaters etc), the maintain a decent loading on them.
During the maintenance visits we would keep an eye on the running time of each engine and decide which engine should be the main one (No.1) until the next visit. It would not be uncommon for a genset to run for 3 or 4 months constantly. ( we have long running oil sumps on each one)