Hi lads, in most of the installations I would be involved with, we have diesel generators suppling all our equipment. In one particular station it was reported that the lights were constantly flickering. This flicking has being going on for a number of years with no known damage and only when the gensets were suppling high loads. Now that more and more electronic equipment is being added to the station, it was decided to look into this flickering more. So, recently I re-wired the 3 generators and replaced the AVR's. (Automatic Voltage Regulators). The mains output cables were checked and secure. When this work was complete a Voltage Monitor / Logger was installed for a number of days. This was to record every 10mS the condition of the AC from the gensets and each genset was run for equal amounts of time and loadings.
The flickering contined to happen when the gensets were suppling high loads ( + 50Amps ) and we then checked the Voltage logger. The frequency was a constant line (48.5Hz to 52Hz), which we are happy with as our controls allow between 46Hz and 54Hz before shut down. Voltage was also ok with the expected volt drop and raises during high or low load periods (210Vac to 245Vac is exceptable to our control cabinets before shut down). AVR's are set to supply voltage at 230V at 51Hz, we go slightly over the frequency because it will drop down a little during high loads.
I then checked all the wiring / contactors / relays , you name it, it was checked in all control cabinets. The flickering continues to happen.
The gensets are all Neutral / Earth linked, single phase, also recently serviced ( Stripped down and re-built )
No motors would be running or any other equipment on except your normal domestic loads (TV, fridge etc)
Any one with any ideas where this flicking effect is coming from. ?
The effect is seen on fluorescent and incandesent lights and the Electronics guys are worried about damage to thier equipment.
The flickering contined to happen when the gensets were suppling high loads ( + 50Amps ) and we then checked the Voltage logger. The frequency was a constant line (48.5Hz to 52Hz), which we are happy with as our controls allow between 46Hz and 54Hz before shut down. Voltage was also ok with the expected volt drop and raises during high or low load periods (210Vac to 245Vac is exceptable to our control cabinets before shut down). AVR's are set to supply voltage at 230V at 51Hz, we go slightly over the frequency because it will drop down a little during high loads.
I then checked all the wiring / contactors / relays , you name it, it was checked in all control cabinets. The flickering continues to happen.
The gensets are all Neutral / Earth linked, single phase, also recently serviced ( Stripped down and re-built )
No motors would be running or any other equipment on except your normal domestic loads (TV, fridge etc)
Any one with any ideas where this flicking effect is coming from. ?
The effect is seen on fluorescent and incandesent lights and the Electronics guys are worried about damage to thier equipment.