I dont know much about electrics.
Here is the issue.

Electric tripping (not blowing) consistently after about 1.5 hrs.

We narrowed it down to one of the fuzes on the box. When we turn that off the rest is fine. We have unplugged everything systematically from that line to try and find out what it is but nothing seems to be stopping it from tripping.

Whats on the line is the kitchen, and study, so not the boiler.

What would you look for next? Do we find the cables to check for rat bites? (or would this make it trip instantly? Not worth doing?)

Could it be the box / commercial unit?

We called out an electrician once and he disconnected the outside light that was on that line too, but still tripping, and we cant really affort to get out another one.

If you could help me at all that would be hugely appreciated. My dad wants to pull up the floorboards and check the cables. So any advice if this is a good idea or not, or what you would do. Any help would be great really.
 
Hi, Thanks for replies.

Yes we did get a sparkie. he said it was on the nutral side, not the live side. Not sure what that means really. And he unplugged the outside light leaving just all the stuff plugged in in the kitchen and study and 1 bedroom on the line which we then turned off. I didnt know that about having to actually unplug them so thats really handy. Ill unplugg everything again and see.

We have had some leaks in the bathroom recently which I thought had been fixed. So if it still trips after I unplug everthing from the socket, does that mean it must be some sort of water in the walls. What does it mean that its neutral? does that mean its an applience? Or could it possibly be water damage still? The fact that it trips after 1 - 2 hours, makes me worry that its water damage which would be very expensive to fix I guess.
Also Im in south wales, near carmarthen. Thanks again
 
Welcome, What is it that is tripping, RCD, or MCB? Whatever your House sounds like it needs testing by a competent Electrician, did the Electrician carry out any tests, or was it a hit and miss sort of job?
 
Any idea how old your electrical installation is?
and as @Pete999 says what is actually “tripping”? Post some pics up........but bare in mind it’s nearly Friday evening o_O
 
Last edited:
.but bare in mind it’s neatly Friday evening
577d96e283e8309cb7ce6feb224e58e7.jpg

beer oclock for some people ,and wine for the gentry people ,what what .
 
It's the gray one in the middle that's tripping only. 1991 electrics were done. And the electirican didn't do a full check, we thought it was the outside light at that point.
 
methink OP should ost his location, may be 1 of us reprobates colud be close and pop over for nominal fee (few pints diesel and a couple gallons beer. , or is that wrong way round? )to investigate
 
bloody big area is wales. i could only cover the north, anywhere south of wrecsam is bandit country to me.
 
What is meant by a neutral fault can be thought of in this way
The trip switch at your mains is sensitive to the balance of current flow down the live and back via the neutral, if its not balanced some is leaking to earth

A neutral -earth leakage via the fixed wiring or a appliance is high enough that it causes operation of the trip

Usually its an appliance that causes the tripping,in the case of delayed rather than instant tripping the main culprits are usually freezers and fridges
If you run a extension lead from the neighbours and try finding the problem by process of elimination

Paying someone to find a fault and being left with same problem is very annoying,unfortunately people get called electricians when they have no right to such a title
If you do bring in another,be aware he needs to make use of test meters or you are being ripped off once again,its not the sort of problem that can avoid their use
 
Has this happened since or a little while after the leak you mention? I ask as I suspect that it may be that there is some residual moisture in a socket below the leak that may be causing the trip. You might pull the fuses one at a time and see exactly which circuit it is on that way. And perhaps tell us if it stops tripping and on which circuit it stopped tripping on.
 
nothing todo with next door's cannabis farm, linked trough attic space.
 
Shister, call out the Marines. I'd be questioning the supplier who installed that meter!

Has this happened since or a little while after the leak you mention? I ask as I suspect that it may be that there is some residual moisture in a socket below the leak that may be causing the trip.


Have you perused the image OP attached? We best stop here.
 
most likely a neutral to ground fault/leak
If you know everything connectted to this circuit ?
Then isolate them completely from the circuit one by one
then see how the circuit holds up
most likely one of them is the culprit
If everything is isolated and it still does it ?
Then it's in the wiring.
 
everything to right of meter to go in bin. Head to be refitted by DNO. then a new CU and full inspection & test. sssimpless.
 
I cannot see where your main protective Earth comes from. It is not from the supply cable, so I assume it is a TT installation that requires a separate Earth/Ground rod - but no sign of the incoming Earth bond wire. As someone said earlier - if the elcb/RCD is OK, then a 100 mA leakage fault is seriously bad news. You do need to get a qualified electrician in who has the knowledge and required test equipment. If the problem is in bathroom or kitchen and the water pipes are being used as the Earth, then you have a potentialy serious electric shock/electrocution situation, in my opinion.
 
I cannot see where your main protective Earth comes from. It is not from the supply cable, so I assume it is a TT installation that requires a separate Earth/Ground rod - but no sign of the incoming Earth bond wire. As someone said earlier - if the elcb/RCD is OK, then a 100 mA leakage fault is seriously bad news. You do need to get a qualified electrician in who has the knowledge and required test equipment. If the problem is in bathroom or kitchen and the water pipes are being used as the Earth, then you have a potentialy serious electric shock/electrocution situation, in my opinion.

I think it’s too late, he’s not been on line for quite a while :fearscream::ambulance:
 

Reply to Hello can you help me fix my house? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
1K
Hi I have a 3phase shop in a high humidity area in (Hawaii) and I'm having some issues with low voltage on the single phase outlets on the 120v...
Replies
6
Views
919

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock