installed a tub for m8 (second hand).

switch on tub runs for about 10 seconds then trips.

clamped up draw initially 3.3A -12.2A when heater kicks in.

disconnected heater unit IR test 400M ohms, 23 ohms heater resistance.

disconnect pump one hot tub will stay on, disconnect heater & leave pump one on hot tub will run but did trip once after about 20 mins.

pump one
checked capacitors 16m farad good, 40m farad good. checked windings brown to blue 11.08 ohms, black to blue 11.10 ohms. IR test to earth 400M ohms.

disconnect plugs for ozone still trips, blower still trips & light still trips.

my findings hot tub turns on timer runs down pump one starts draw around 3amps heater kicks in around 12amps then trips after about 2-3 seconds later thinking I have a earth fault under load or am I missing something ?
 
Guessing it's the 30mA RCD that trips - ramp test it? Measure the earth leakage at the tub. When heater IR tests were done, was the tub in working condition with water etc. Results so far seem to point to heater, but that's not backed up by the IR test :( . What is the earthing arrangement (just interested) and has the tub been working ok for a while, or is this maybe why the previous owner sold it on?
 
installed a tub for m8 (second hand).

switch on tub runs for about 10 seconds then trips.

clamped up draw initially 3.3A -12.2A when heater kicks in.

disconnected heater unit IR test 400M ohms, 23 ohms heater resistance.

disconnect pump one hot tub will stay on, disconnect heater & leave pump one on hot tub will run but did trip once after about 20 mins.

pump one
checked capacitors 16m farad good, 40m farad good. checked windings brown to blue 11.08 ohms, black to blue 11.10 ohms. IR test to earth 400M ohms.

disconnect plugs for ozone still trips, blower still trips & light still trips.

my findings hot tub turns on timer runs down pump one starts draw around 3amps heater kicks in around 12amps then trips after about 2-3 seconds later thinking I have a earth fault under load or am I missing something ?
Well if you are getting those sort of insulation resistance readings it no wonder the tub is tripping out. What is actually tripping CB or RCD?
 
Hi Pete
VIR
230 V
10.3 I
23.3 R
sorry am I having a blond moment heater is 2.5kw.

400M ohms IR test to earth good
23.3 ohms heater continuity
 
Guessing it's the 30mA RCD that trips - ramp test it? Measure the earth leakage at the tub. When heater IR tests were done, was the tub in working condition with water etc. Results so far seem to point to heater, but that's not backed up by the IR test :( . What is the earthing arrangement (just interested) and has the tub been working ok for a while, or is this maybe why the previous owner sold it on?

good idea I will ramp test RCD & check the leakage of the trip with tub on & see the spike. will check Monday, did not think RCD as know the house no issues with RCD to date. TNCS
 
my thoughts at guess at one point heater had small crack in when heating let water past but heater has water around it all the time so can't see it especially with the IR value being good.
 
Well if you are getting those sort of insulation resistance readings it no wonder the tub is tripping out. What is actually tripping CB or RCD?

Hi Pete
VIR
230 V
10.3 I
23.3 R
sorry am I having a blond moment heater is 2.5kw.

400M ohms IR test to earth good
23.3 ohms heater continuity
did you spot something that in the above that I may have missed ?
 
Hi - understand, I have seen where RCD is a bit sensitive and a few mA is already there from other appliances on the circuit (?).
be quite honest there is only 3 items on this side of the board & hardly any equipment installed apart from usual fridge wash machine few sockets, not really much in Bungi
 
Had a similar problem on a Sauna some years ago, IR test all good but within seconds of the heaters kicking in the RCD would kick out.
Turned out that it had been sitting in a warehouse unused for a while & the elements had got damp in them.
 
Had a similar problem on a Sauna some years ago, IR test all good but within seconds of the heaters kicking in the RCD would kick out.
Turned out that it had been sitting in a warehouse unused for a while & the elements had got damp in them.
Hi Thanks for that specialist
as above I will disconnect heater & power supply from tub probably use a 16amp CB inline at tub whilst I am there disconnecting & then turn on heater direct through 16amp CB, hopefully will trip or heat up.
 

Reply to hot tub fault tripping after switching on in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, My hot tub keeps tripping after 12 years of use. I'm thinking it's the GFCI gone bad. Unfortunately it's a CH 2 pole 50 amp (GFTCB250) and...
Replies
1
Views
884
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
846
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock