Hi I have recently purchased a 1970s semi detached house and had a full rewire and new central heating system installed by separate companies. There were a few things I was concerned with and am hoping to check with some qualified electricians before I bring it up with the electrician - I have no knowledge of electrics so for all I know the work might actually be ok.

1. The new wires that have been run under the floor upstairs are touching the copper water/central heating pipes in places is this ok? I am worried about heat damaging the cable. If this is not ok how should this be remedied - would it be the plumbers who put this right or the electrician?

2. I have requested mains smoke alarms be fitted in all rooms. At the back of the alarm where it connects to the mains the electrician has put all of the terminals in choc boxes (correct term?) however one smoke alarm just has the conductors going into the terminals with nothing around it - is this ok or should it be housed in a box?

3. Lastly under one of the bedroom floors the plumber went through a mains cable so the electrician fitted a junction box. I was worried as I had read that maintenance free junction boxes should be used in inaccessible areas - should I ask him to change this for a maintenance free one. I did ask him but he said the junction box is ok

Any advice would be greatly appreciated. Many thanks
 
That connection of the smoke detector is appalling you should never have exposed wiring and connectors like that, "choc boxes" will not comply with the others because wiring from the detectors will still be exposed. They should be mounted on some kind of box to enclose it all or opt for detectors which do not require a separate connection from the detector.
 
If he has used a junction box without maintenance free connections in a floor space this will not comply. Me I would want the whole length of cable replaced as this is a rewire and joint boxes should be avoided. Has he actually supplied Certification to say this is a compliant installation because as it stands it is not.
 
agreed but the wires that come with the detectors are single insulated, unsheathed, so what can you do? i just fit line products "eggs", but then the hole in the ceiling is so large, you have trouble getting a fixing for the detector. think the detector manufacturers need to come up with a better design. maybe a terminal strip that T/E and 3 core/E will fit direct.
 
agreed but the wires that come with the detectors are single insulated, unsheathed, so what can you do? i just fit line products "eggs", but then the hole in the ceiling is so large, you have trouble getting a fixing for the detector. think the detector manufacturers need to come up with a better design. maybe a terminal strip that T/E and 3 core/E will fit direct.
They will fit to a one gang cavity box but the best are the ones you hard wire direct, the name skips my mind.
 
a lot of things skip my mind these days, but i blame dementia. as long as i know the price of beer, i'll let some mundane things pass.
 
Not only that looks like he has mounted the smoke alarm with just screws through the plasterboard! No fixings at all?

On every job I do I am always removing choc blocs and replacing them with something more suitable. By the end of the week my pockets are full of the damn things.
 
Hi

Thanks for your message. Yes we received certification for the work. Another quick question if you don't mind.

In the majority of places the joists have been drilled and the cable runs through these holes. In one bedroom however the cable runs over the top of a piece of wood and rests on the top of the plasterboard ceiling of the room below. I'm not sure if it hasn't been drilled because the piece of wood is very thin -its not like the wood in the rest of the rooms. Is this ok or should the wood be drilled and the cable run through or alternatively clipped to the side. I don't want to bring it up with the electrician if this is normal policy. Picture attached. Many thanks

joistcable.jpg
 
Hi

Thanks for your message. Yes we received certification for the work. Another quick question if you don't mind.

In the majority of places the joists have been drilled and the cable runs through these holes. In one bedroom however the cable runs over the top of a piece of wood and rests on the top of the plasterboard ceiling of the room below. I'm not sure if it hasn't been drilled because the piece of wood is very thin -its not like the wood in the rest of the rooms. Is this ok or should the wood be drilled and the cable run through or alternatively clipped to the side. I don't want to bring it up with the electrician if this is normal policy. Picture attached. Many thanks

View attachment 37115
a bit slipshod there. cable should at least have a few clips in to restrain it. but it's OK over that noggin.
 
The detectors will have come with a base as standard that contains a connector strip to wire into and the smoke head will fix on to the mounting base enclosing all connections.

how anyone can f**k that up god only knows!
most come with a 3 wire plug in lead that you have then to connect to your 3 core and T/E.
 
I don't think it was cheap - £3500.

Can i also ask about the mains wires touching the central heating pipes - is this ok or should they be clipped away from the pipes or can the pipes have insulation around them? If it is a problem is this something the electrician or central heating installers should do? Many thanks
 
I don't think it was cheap - £3500.

Can i also ask about the mains wires touching the central heating pipes - is this ok or should they be clipped away from the pipes or can the pipes have insulation around them? If it is a problem is this something the electrician or central heating installers should do? Many thanks
What came first the pipes or the cable.
Reg 528.3.1, A wiring system shall not be installed in the vicinity of services which produce heat, smoke or fumes likely to be detrimental to the wiring, unless it is protected from harmful effects by shielding arranged so as not to affect the dissipation of heat from the wiring.
Reg 528.3.3 refers to any foreseeable operations carried out the other service will not cause damage to the electrical service or the converse.
 
Under the floor in the bedrooms cable had been run first then pipes were put in afterwards. However in the bathroom - image attached the cable would have been put in after as the central heating company did not replace a section of the copper pipe in the bathroom - image attached. Thanks

pipescable.jpg
 
I don't think it was cheap - £3500.

Can i also ask about the mains wires touching the central heating pipes - is this ok or should they be clipped away from the pipes or can the pipes have insulation around them? If it is a problem is this something the electrician or central heating installers should do? Many thanks
all depends who was there first. if the cables were installed first, then the plumber should keep his pipes away ( min 25mm). if the pipes were there first, then it's up to the electrician to maintain separation.
 
Agree with others but should be simple fixes for the electrician, put a few clips in that cable running over the noggin, fit round dry linning box for the smoke alarms (the surface boxes look a bit naff) and put some lagging around the pipe were the cables are in close proximity , just a bit of basic snagging that should of been done at the time of the rewire
 
Thank you for all your advice. I will ask about getting a round dry lining box for the smoke alarm in the picture. The other smoke alarms have a box taped around the connections (please see image attached) is this sufficient? The box doesn't seem to close properly hence the tape. I'm not sure what the boxes around the connections are needed for so was worried that if one of the reasons for the box is to prevent fire spread having the box slightly open would defeat the point....

boxalarm.jpg
 
Hi Jo: Good pictures.
When was the house re-wired ?.
If you've recently paid for a re-wire, I'd love to hear your Electricians explanation for Re-using old cable.

Love the Blue tape and the way the cable sheath doesn't enter the box.
 
Apologies Jo: Forget what I said said about old cable, just viewed the picture on my daughter's laptop & the cable shows up as Brown / Black as it should do. It's modern 3 core, guess it's time to send this tablet back :(
 
Last edited by a moderator:
It's just all a bit lazy. Lack of pride in your work and 'if things can't be seen then they don't matter'.
If the OP can take photos of the things she feels to be wrong then it dictates the possible standard of the rest of the install.
Very most probably safe but with a lack of good standard.
If the installer ever sees this, know that we are not impressed and as mother would say 'buck up your ideas'
 
Just insist that the so called "sparks" replace the smoke alarms with ones made by Aico - then all the connections are within the casing of the unit and accessible...
 
Hi Jo. Concur with the good advice given. Some of the pics you've posted don't look too good (#2 &26). With the advice given, why don't you come up with a snagging list, and submit them to your electrician, and ask for them to be rectified. If the electrician declines you may be able to take it further, if he/she is registered with a scheme?

The design of smoke alarms (ones I've fitted anyway) are poor for wiring connections, but something better could of been achieved in your case. As per cables in close proximity to non electrical services, achieving separation is often difficult to achieve in a rewire & re-plumbing, as generally not all of the flooring can be removed to ensure all cables/pipes are routed as such and clipped.
 
Agreed this is rough bit nothing more than a snagging last is required. Easiest thing in the world to sit here and slate people's work. As for the cables over the noggin why would you clip these as they are under the floor and unless you are going to lift every floor board and clip every cable you are wasting your time. The spark was there first so the pipe can't be blamed on him. So we are actually looking at removing some choc blocks not exactly the snagging list from hell
 
Apologies Jo: Forget what I said said about old cable, just viewed the picture on my daughter's laptop & the cable shows up as Brown / Black as it should do. It's modern 3 core, guess it's time to send this tablet back :(
or a visit to specsavers. ;)
 
^^ so no part P yet...

As others have commented, you need to draw up a snags list and get them back to review......and agree actions .....
 
Those smoke detectors generally are a poor design, but should fixed into a fast to fix box as previously said with some wagos jointing the cables. Could have atleast put some tape around em

Edit: Also he has not identified the 3 core black and grey as line or neautral
 
I've always fitted the aicos so have brought the cables into the term blocks but I like that idea of the circular fast fix, you and @Flanders mentioned. Would be an easy fit with the number of refitting holes they put in the bases.
 
Are the Aicos the ones where it's still tight to get all conductors in the space and the slide the head on?
Yeh but with just the power then link it's not a bother - you do measure the conductors though and the lid is a hinged affair which helps.
 
Yeh but with just the power then link it's not a bother - you do measure the conductors though and the lid is a hinged affair which helps.

Ahh not the ones I've fitted in the past then which have been a right pain in the arse (think in a blue box?) been a few years. A fast to fix with a couple of stuffing glands in can't be beaten, a few extra minutes for less hassle and a top notch job (unless ins latt&plaster then It's a c**t.)
 
I use some form of back box with Aico, nightmare to terminate properly otherwise. They've allegedly changed the design, to making the connections more easier!
 
I use some form of back box with Aico, nightmare to terminate properly otherwise. They've allegedly changed the design, to making the connections more easier!

Why do you need a back box? Bring the cable(s) through the ceiling, connect to visible connectors...... If the cable is a bit long, push a bit back into ceiling void. Simples
 
Why do you need a back box? Bring the cable(s) through the ceiling, connect to visible connectors...... If the cable is a bit long, push a bit back into ceiling void. Simples

Well, the distance between terminals and base plate is minute, so stripped back cables are exposed behind fitting, however careful you try to be. Back box for me.
 

Reply to House Rewiring Compliance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
892
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
778
After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
737
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
363
Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
956

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock