Simple little fault N to E fault , checking the wiring a junction box had 11 twin and earths entering so off with the lid checking all the wirng all seamed ok continuity reading of 0.19 accross the N an E with the circuit disconnected at the board ,so disconnect each neutral and check till i found the fault went through then all found the cable pulled the wire nothing on the end of it fault was a touching N and E , great easy you thing , well no red wire connected to the neutral mm , follow that went to an outside light so checking again it went to the passage way wall lights to the live terminal ES lampholders nice incorrect polarity what i thought was the outside light wasnt the neutral wire went to to out side light the live wire went to the live of the switch , the outside light was wired live to live via the switch and it worked but had a 150 lamp in probably due to it glowing , then finding 6 500 halogens on the same circuit arghh it was a night mare ,so labling and marking the wires and 5 hours later it appears to work
Reply to how a small fault can lead to a can of worms in the Australia area at ElectriciansForums.net
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
8K