How would you go about changing this unit over?

819FE7C3-DD6D-42A6-8F5D-C87DFF9CB94C.jpeg


Old wylex board with Pyro mains tails. Earthed via Pyro, and all circuits via conduit.

Protrudes out the wall so I was thinking 1 of options, as I can’t see any other way round it.


Option 1
Batten on each side of the DB to the same level of the current one, crimp all cables and mount new unit over the old one.
Take a 16mm cpc from old board to new board.

Option 2
Angle grind the DB so it’s level with the wall and do same as above.

Option 3
Remove current DB completely and try to get another one in the same space, attempt to alter conduits and pyro to fit.
Don’t fancy bending pyro!
 

Attachments

  • 07D8528B-7DCC-4217-B602-892FD75F2449.jpeg
    321.1 KB · Views: 84
  • CEE0A6FF-92CF-40FF-A0DB-39BF30776208.jpeg
    380.5 KB · Views: 82
You could get another one in, would need to dig the wall out quite a lot though. Id use a Hager board, the model with no knockouts.

I've seen people fit new boards on top of old ones, but I've never seen that done in a way I'd consider satisfactory. Those conduits are probably 3/4 inch.

Edit I've just seen the conduits are at the bottom and top of the enclosure, I'd probably cheat in that case, cut the enclosure flush with the wall then mount a new cu on top. Not ideal but there is little else you can do without digging the conduits right out of the wall to adjust them to the new cu height.
 
How would you go about changing this unit over?

View attachment 64229

Old wylex board with Pyro mains tails. Earthed via Pyro, and all circuits via conduit.

Protrudes out the wall so I was thinking 1 of options, as I can’t see any other way round it.


Option 1
Batten on each side of the DB to the same level of the current one, crimp all cables and mount new unit over the old one.
Take a 16mm cpc from old board to new board.

Option 2
Angle grind the DB so it’s level with the wall and do same as above.

Option 3
Remove current DB completely and try to get another one in the same space, attempt to alter conduits and pyro to fit.
Don’t fancy bending pyro!
Option 2
 
Unless you start talking rewire, it's adapt the existing box with the conduit entries.
I'd be checking the load and size...that pyro term looks a bit sweaty.
Is it a flat?
Interesting for a domestic job. Quite costly for a board change.
 
With the local tranny, even the doorbell system is wired via the conduits. Well done, originally. Probably local authority.
 
Cheers guys, I had already opted for option 2 if I get it, I just always wonder what other people would do in these situations.
It’s not ideal, but the only way round it really without a rewire.

If I end up doing it I’ll post up pictures!

Its a tiny ex-council studio flat, with a 60a isolator, load isn’t an issue for what’s currently in there.
 
Remove the guts, fit a din rail on standoffs with standard main switch and compact RCBOS, mount a neutral bar in the back of the enclosure on insulated standoffs. Make a nice cover out of polished brass plate a little larger than the box, bevel the edges of the plate for decoration. Drill fixing holes to match the existing lid lugs and cut out a rectangle for the devices to poke through. make a hinged cover to go over circuit breakers, formed again from brass plate, this time shaped with an industrial press. Fit lid to enclosure using copper or brass dome head rivets. Etch the brass with circuit information, filling the etched parts with dark blue enamel paint. Polish and fit cover with new brass pan head machine screws.
 
Cheers guys, I had already opted for option 2 if I get it, I just always wonder what other people would do in these situations.
It’s not ideal, but the only way round it really without a rewire.

If I end up doing it I’ll post up pictures!

Its a tiny ex-council studio flat, with a 60a isolator, load isn’t an issue for what’s currently in there.
Good choice,& yes a rewire would be better,& a recommendation to the client.
 
Unless the board change was part of a full rewire I personally would not entertain it.
i have come across them where the electrician butcher / mount a new plastic board over the top and try to extend the old wires using crimps and connector block etc but look dog rough With loads of mastic and no nails holding them on.
 
You could make a decent job of this by fitting a timber frame around the old Wylex enclosure, extend circuits properly and carefully as required in the empty enclosure then mount the new CU on a nice piece of ply fixed to the new timber frame.
 
Cheers guys, I had already opted for option 2 if I get it, I just always wonder what other people would do in these situations.
It’s not ideal, but the only way round it really without a rewire.

If I end up doing it I’ll post up pictures!

Its a tiny ex-council studio flat, with a 60a isolator, load isn’t an issue for what’s currently in there.
You cannot grind a CU down as you suggest. You are now the designer if anything should happen.

I'd price to do the job properly or not at all. Either way its not the usual (for here) £200 CU swap.
 
I think a Wylex skeleton CU would be an option to fit into the existing enclosure, if it would fit it would be the neatest outcome IMO
Great idea if it fit. If it doesn’t what then?

Is it permissible to use different components from different manufacturers to build a board?


im surprised there isn’t something out there ready designed for this issue as it is not uncommon.

Don’t like doing Frankenstein jobs but in this instance I don’t see how it can be avoided, but in doing so are we breaking our regs.

Personally I would either do a full rewire or walk away. But I would let customer know there could be electricians out there who are willing to do a Frankenstein job.

im not criticising either option, just giving my take.
 
Doing a full rewire through all singles in existing conduit will make no difference to the situation, unless you ditch that and chase t&e in everywhere.
 
Last edited:
You cannot grind a CU down as you suggest. You are now the designer if anything should happen.
I don't think they are suggesting grinding down the replacement CU, I think it is to level the old metal to the wall and then mount a new external one over the top.

In that case the old CU is simple a large box and the only real issue would be safely and professionally extending the cables to reach in to the new CU. For most of the cables probably MF boxes would do if the fit in the remains of that old CU behind.

Not so sure about the pyro, but I would be inclined to use bare crimps and glue lines heat-shrink to extend the pyro's tails. At 60A and enclosed as it is you could use 16mm tri-rated for that, assuming proper crimps and ferrules to match.

But I might have missed something blindingly obvious here.
 
Actually one blindingly obvious thing just after posting is the pryo cables might be a lot less than 16mm so common crimps won't be OK as they are not size-converting.

Might be a job for a couple of big DIN terminals?
 
The best option would be, giving that the client would have to forebear decor etc, carefully dig out the CU, keep all existing lock rings/lock nuts in case imperial sizing, obtain a cu with no knockout's, make up template and pre drill for conduit entries, refit existing lock rings/lock nuts hence no need for joints etc, like for like retermination.
 
The best option would be, giving that the client would have to forebear decor etc, carefully dig out the CU
That would be ideal, but given there is conduit entering both top & bottom it might be difficult/impossible to remove the old CU, or indeed find one to fit the same conduit-conduit spacing that can be inserted again and conduit attached.

I see a whole lot of re-threading pain going down that route...
 
That would be ideal, but given there is conduit entering both top & bottom it might be difficult/impossible to remove the old CU, or indeed find one to fit the same conduit-conduit spacing that can be inserted again and conduit attached.

I see a whole lot of re-threading pain going down that route...
Yes difficult, without seeing the job it's hard to see a good solution.
 
Great idea if it fit. If it doesn’t what then?

Is it permissible to use different components from different manufacturers to build a board?
It's a Wylex 3036 board if a Wylex skeleton board fits in the enclosure your not mixing different manufacturers components
im surprised there isn’t something out there ready designed for this issue as it is not uncommon.

Don’t like doing Frankenstein jobs but in this instance I don’t see how it can be avoided, but in doing so are we breaking our regs.

Personally I would either do a full rewire or walk away. But I would let customer know there could be electricians out there who are willing to do a Frankenstein job.

im not criticising either option, just giving my take.
The problem is some of these sites were originally a bespoke solution for each developer, 60 years on and an adapted solution is the only way to replace them

Not sure why you term this type of job a Frankenstein job is it because there is no out of box solution
 
Whats made it a ball ache, using threaded conduit entry with lock ring and a female bush, that is rubbish I always use socket and male bush for this type of install.
Done 50-60 years back........maybe they ran out of mb bushes or couplings. Just a couple of lads dropped off on the job, stuck in the middle of nowhere, no van, no phone..........and they don't know the code for smoke signals....give 'em a break for using their initiative. ?
 
I don't think they are suggesting grinding down the replacement CU, I think it is to level the old metal to the wall and then mount a new external one over the top.

In that case the old CU is simple a large box and the only real issue would be safely and professionally extending the cables to reach in to the new CU. For most of the cables probably MF boxes would do if the fit in the remains of that old CU behind.

Not so sure about the pyro, but I would be inclined to use bare crimps and glue lines heat-shrink to extend the pyro's tails. At 60A and enclosed as it is you could use 16mm tri-rated for that, assuming proper crimps and ferrules to match.

But I might have missed something blindingly obvious here.
Sorry. I read it as cutting the back out of the new Cu to fit over the old one. My bad - as the youngsters say ???
 
Not sure why you term this type of job a Frankenstein job is it because there is no out of box solution
Frankenstein job is basically taking components from different sources that where not designed to go together and adding them together to or incorporating into an older product.

So yes, “no out of box solution” that’s about the reasoning behind it.
 
rip out the innards. fit din rail, main switch and RCBOs . get a lid fabricated, (needn't be too fancy, any F**k ups will be covered in stickers anyway),
 
I did contemplate that Telectrix but unsure how BS would take to my own line of DB production.

Its a small studio flat, the landlord isn’t going to pay for a full rewire, especially when it doesn’t need one.

Turning the original box into a junction box with proper crimps/no maintenance joints, and then mounting over would look quite decent in my opinion.
Regarding using a grinder, it would only be to bring the existing box level with the wall to get a neater finish.

I get the whole walk away from the job mind set as I’ve done it many times before, but I don’t think it applies here when a satisfactory result can be had without going full rewire.
 
You'd probably find that the band saw would be better than a grinder as there won't be any sparks.
 
The difficult bit is that the existing is a surface fuse box that has been partly flushed in, If it was all surface or fully flushed in it would be much easier!
 
Better to leave that protruding and batten round the edges in order to fix a flat piece of ply for the new CU. It would give you more wiring space in the old enclosure in behind too.
Most simple method, by far.

It makes me think, though. What extra work has been done, points wise. The number of outlets needed, these days, compared with the 60's doesn't bear thinking about. Looks like one ring and a cooker. I could see at a couple of 4 way extension leads around. Probably OK if not in a kitchen, though.
Wonder what that 2.5 is from the 5amp.
 
The 2.5 was supplying a switch and socket on one of the walls.
I'm guessing it was intended to be a 3pin lamp plug and it has a normal light switch, but somebody decided to swap it over with a normal plug or just installed a normal plug instead!

Tenant told me it kept blowing the fuse wire when he plugged the hoover in and he lost his lights as well ?

As said, its a small studio, 4 x single sockets in the main living/bedroom area, 13a oven, a washing machine/tumbledryer all in one unit, a 3kw immersion heater and a few other bits like an extractor fan etc.
 

Reply to How would you change this. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
597
Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
856
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
234

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock