the question i am struggling with is this, im new to the calculating of things and am not sure where to start.
A two core cable supplies two loads from a 230v supply, the first load is 70m from the supply and takes a current of 40A, the second load is 100m from the supply and takes 20A. find the voltage across the second load if each core of the cable has a c.s.a of 25mm2, assuming resistivity is 17M ohm mm.
Try breaking the cable down into two, do some calculations as post your answers...
You have got a slightly difficult one there since it is not the standard on site method of VD= (mV/A/m)*1000*A*L
The value for the resistivity (rho) should be 17 mohm.mm
Since the SI value is 1.7*10 to the power of (-8) ohm.m
Calculation is R= rho* L/A using SI units (Ohm= ohm.m * metre / Amps)
and V=IR
Try this and see how you get on doing as Strima says.
Reply to If anyone could give me their answer on this question, and how they got there pls in the UK Electrical Forum area at ElectriciansForums.net
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
This is a question with probably so many answers and solutions, but I wondered how people would do it. I have a clients house which already has...