Job done.

Pic of the shed shows what I was on about – I wanted to run an RFC all around the perimeter.

But OK, I’ve listened, and changed my mind. I installed it as two separate radials, on two 20A breakers, rather than as a single ring on one 20A.

I believe it's electrically not as sound as my ring proposal (the CSA is lower), but I agree more ‘standard’. An example of where strict compliance with regulations is actually worse electrical design than ‘breaking’ the rules.

Also a pic of using SY for the sockets but without the correct SY glands, designed, I believe, primarily for where EM screening is specified.

Unravel the screen, twist, sleeve g/y, then shrink-fit the lot. Outer sheath ends in a normal cable gland. Is this OK? BTW, the holes in the back of the metal boxes will be sealed to keep insects out. Not fitted the accessories yet, and though I’d better consult this wise oracle before proceeding …

Thanks, Mark.

DSC_5632.JPG DSC_5633.JPG
 
Im assuming this may be for FLT batteries iv seen them done with busbar a few times dependant on the load

Only concern I may have would be the "wosk area" and any welding ect in the presence of battery fumes ect
 
Im assuming this may be for FLT batteries iv seen them done with busbar a few times dependant on the load

Only concern I may have would be the "work area" and any welding ect in the presence of battery fumes ect

I was asked this before.

Naa, they are only for ordinary batteries: cars, lawnmower, motorbike, children’s quads, that sort of thing. Nothing big. And only little ‘Accumate’ maintenance chargers to stop the batteries self-discharging when left for a long time.

No hydrogen gassing off to speak of.

Massively envious of your 'shed'!

Thanks Archy. I like my shed too. The only way I can afford admittedly ridiculous projects like this is by doing everything myself. Which is one reason I’m on here asking questions … :)

Oh, and the other thing is to buy nearly everything on EBay, and to throw away your Tv.
 
........... is by doing everything myself. Which is one reason I’m on here asking questions … :)

Absolutely, go for it! (as long as you comply and get by the Notification Police (sarcasm can be taken as read there))

Oh, and the other thing is to buy nearly everything on EBay, and to throw away your Tv.

Ebay is my friend too. Need to get unhooked from trawling Electricians Forum next!

ghjdjuyhdtyjgutdrse6vbaew
 
Hi,
Don't lightly solder where screw terminals are concerned, the screw pressure over time will cause the solder to cold flow. Have a look at farnell part number 1121755 for the correct item to use.
 
Hi,
Don't lightly solder where screw terminals are concerned, the screw pressure over time will cause the solder to cold flow. Have a look at farnell part number 1121755 for the correct item to use.

Thanks - Very good advice about the cold flow.

I already ordered some 6mm (yellow) twin-entry ferrules, which two x 2.5mm SY cores fit nicely, but once crimped they won't go into the terminals!

The Farnell site is not clear on the spec of 1121755. Is that TWO x 2.5mm cables or 2.5mm TOTAL CSA?

I don't want to remove strands if it can at all be avoided.
 
Most likely me Mark, but I see a load of yellow and green cables there but not a brown in sight. I see where you have heat shrank the braid ok, I see a couple of Blues and then 4 what look like CPC coloured cables ..........
 
malc, there is 2x brown, but it looks like a black in the flash. 2x neutrals, 2 x CPC and 2x braiding
 
images


Lol I still can't see them, but take your word for it mate
 
It is designed for 2*2.5mm to sit side by side.
 
Thanks, John! Yes, Malcolm it is you: I reckon you've had too much desert sun :) Or you need a new monitor ...

It is pretty poor sleeving, from TLC. All a bit stuck-together and floppy, I don't like it much. I prefer to shrink-fit cable ID markers, but it's a waste of money for all that lot, which no one will ever see again.
 
It is designed for 2*2.5mm to sit side by side.

OK. Ordered on-line just now!

Malcolm, joking apart, this is a massively interesting psychological effect, especially relevant when quality-assuring one's own work in many trades. Can you really not see those two brown cables? They are quite clear and absolutely in your face!

I can't remember what the effect is called, but I know psychologists have studied it. There is a book by Prof Richard Wiseman called ‘Paranormality: Why we see what isn't there’ which touches on it. Something about the 'gorilla in the room'.

Subjects are shown a video of people arguing in the street or something, but no one, when debriefed afterwards, remembers seeing the guy in a gorilla suit walking by. But he's there and absolutely clear. I reviewed the book on another forum where I annoy people:

On all things wondrous strange: ghosts, mediums, and rubber hands - Mark Ribbands - RichardDawkins.net

It’s all very fascinating.
 
Last edited:
To me they look like 2 conductors covered in black heat shrink/sleeving/neoprene, they don't look brown at all but there again I have old eyes
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Mark42

Patron
~
Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Large number of 13A sockets in a steel building: Design considerations.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
Mark42,
Last reply from
malcolmsanford,
Replies
34
Views
9,112

Advert