Spannaz

Hi Guys,

Just been to do a Condition report on a 30 year old installation. Both lighting circuits are wired in twin stranded steel cable with no CPC. The insulation test is good, but with the lack of CPC, and brass accessories, would you consider this as 'Satisfactory'. No RCD on lighting circuits either.
 
Steel cable? Rcd on light circuit to the bathroom? Is there metal conduit acting as cpc?

Nope, nothing acting as CPC. I did the report yesterday and failed it, customer rang this morning and tore strips off me as she's had someone else in and they've passed it. The other big issue is that the Insulation Resistance on the ringmain Line to CPC was 3.4M. OK, just scrapes through...but not good. How can someone pass it. They told her just to use plastic light switches and she'll be alright LOL There is even brass wall lights. I mean....really?!?!?!?!?!?
 
Nope, nothing acting as CPC. I did the report yesterday and failed it, customer rang this morning and tore strips off me as she's had someone else in and they've passed it. The other big issue is that the Insulation Resistance on the ringmain Line to CPC was 3.4M. OK, just scrapes through...but not good. How can someone pass it. They told her just to use plastic light switches and she'll be alright LOL There is even brass wall lights. I mean....really?!?!?!?!?!?

Stick to your first report mate. She may not like it but its your neck on the line.
 

Reply to Lighting circuit with no CPC, fail??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
650
Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
I've tried to research and form a plan without asking on here, but I'm just going around in circles. Just completed an EICR. The wiring ranges...
Replies
15
Views
2K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
450

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock