Hi

I wonder if anyone has any useful thoughts on this. Client wants me to redo consumer unit but doesn’t want disruption to fabric of building. I’ve attached pic - looks like original wiring was a 16mm earth to the live incomer .

The meter box is >20m away.
I guess cable is cable but 16mm would be undersized in a modern installation
I don’t understand why it was done like this since the house was built 2011 from ground up, so no retrofitting.
This is one of two consumer units, both of which have Knx units in same unit (which they shouldn’t) , and will be migrating them to a different system that will work better for the client.
The latter is relevant as it appears the KNX install was done by someone who had no idea, nor the software to programme it all, so none of it works as it should, but is now
67C65FFB-CDAE-4F0B-98DC-9A37E5AA2688.jpeg
 
Last edited by a moderator:
You sure the neutral isn’t blue tape over earth as well?

Badly crimped earth wire in the back and some phone wire?

16mm is fine IF it’s fused appropriately.
At 20m to meter, are these single tails? Protected in conduit or anything?
 
Thanks for prompt response

Neutral probably the same yes but can’t confirm yet
There’s a lot of other dodgy and messy wiring in there, but the rest would reasonably easy to resolve in the consumer unit

Im going back to property today to look at a bit more, as I wrongly assumed there would be no problem to the unit!
But if they are earth cables that have been taped, then that would mean they are single insulated, so would need to be in conduit or something.
Have no idea how I would run new meter tails if they don’t want any disruption to building fabric!
 
What is exiting the incomer meter/isolator/ (kmf?) Clearly, if you’ve proper tails one end and then this at the other then somewhere there’s a join - which personally I’d be more concerned over than the issue of non-compliance (lack of sheath) or questions about sizing.

I’m going to go on a limb of a guess of the back story, here…. There’s a KMF after the meter and proper tails won’t fit the termination, ‘electrician’ then realised that 16mm single wasn’t on the shelf at the wholesaler in anything other than G/Y unless they got a 100m drum in of each colour, special order.
 
What is exiting the incomer meter/isolator/ (kmf?) Clearly, if you’ve proper tails one end and then this at the other then somewhere there’s a join - which personally I’d be more concerned over than the issue of non-compliance (lack of sheath) or questions about sizing.

I’m going to go on a limb of a guess of the back story, here…. There’s a KMF after the meter and proper tails won’t fit the termination, ‘electrician’ then realised that 16mm single wasn’t on the shelf at the wholesaler in anything other than G/Y unless they got a 100m drum in of each colour, special order.
Yes, I’m guessing same, but will give update when get chance to go to property - which I won’t now until Monday as client not available until then
 
Thanks for prompt response

Neutral probably the same yes but can’t confirm yet
There’s a lot of other dodgy and messy wiring in there, but the rest would reasonably easy to resolve in the consumer unit

Im going back to property today to look at a bit more, as I wrongly assumed there would be no problem to the unit!
But if they are earth cables that have been taped, then that would mean they are single insulated, so would need to be in conduit or something.
Have no idea how I would run new meter tails if they don’t want any disruption to building fabric!

As said above probably the only cable they had was std g/y 6491x .

Which would be unsuitable, firstly because it is single insulated, (unless it's run in conduit or trunking over it's whole length); but also because it is prohibited to oversleave g/y as any other conductor.
 
As said above probably the only cable they had was std g/y 6491x .

Which would be unsuitable, firstly because it is single insulated, (unless it's run in conduit or trunking over it's whole length); but also because it is prohibited to oversleave g/y as any other conductor.
I was holding back from the G/Y ident issue until I’d dug out my 16th ed and double checked what we were allowed to do back in 2010! I’ve a sneaky feeling I remember the whole G/Y exclusivity was 17:1??
 
I am sure I remember not repurposing green yellow going back to the 16th.
 
Tbh, I was always taught never to over sleave g/y right back from the late '70s (not that we over sleeved much then anyway)

As you say I don't know when it became "official" but I expected it to be way back tbh.
 
OK made me check, but the red book of 2008 has reg 514.4.2 indicating g/y must only be used exclusively for cpc/earth bonding etc

It was also in regulations B54 and B57 of the 14th edition - although B57 was for all flexible conductors.

Although the earth could be solid green up to 1977 of course.

It also wasn't as specific back then, the regs were more "you understood and applied their meaning " rather then today where they have to spell things out somewhat more.
 
Last edited:

Reply to Live incomer is earth cable wrapped in brown tape? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
Replies
30
Views
4K
Correctly closing off a dead twin and earth cable in a loft. My old house used to have radial circuits serving night storage heaters. Those...
Replies
4
Views
2K
Morning all, Before I start I don't need all the "you're supposed to be a qualified electrician, you need to go back to college' brigade to jump...
Replies
8
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock