I found shortcomings from both electricians, so I am not going ahead with any one of them.

One was the attitude to replace RCBO with MCB if fault can't be rectified, instead he should have said that we must rectify the fault as that can be dangerous.

The second one is the earth bonding. When I told him that the supply pipes are plastic up to the house boundary he said he will leave the water pipe but he will upgrade the bonding to gas pipe anyway.

Strima said that you guys will calculate in this scenario if bonding is required. I read about bonding in the following article.

So it certainly makes a case to do proper assessment and calculation and then bond if required. So that is another thing

I will take few more quotes now because now I know what should I ask. I am fairly sure that old cables and sockets(MK brand) are in very good condition. The only sockets which I have doubt are relatively new ones fitted in the kitchen during kitchen refit about 9 years ago. They are of Lap. One was causing sparks during on/off and blew the fuse. I have changed 3 single Gang sockets with Schneider sockets. I will replace the other sockets in the kitchen too. Is Schneider fine or should I get the MK brand sockets.
May be I should just get an EICR first and if there is a need for rewire then sort that first at the first opportunity and then at the same time do the CU upgrade. If no faults then just do the CU upgrade. The new circuit in the kitchen can wait until that time.

Btw, a lot of you are emphasising on SPDs. I am still not convinced of their benefit in an average city house. Anyway if one has to go with SPD then is it allowed to mix different brands in a CU or not. I know you can't mix different brands RCD/RCBO/MCBs. Whatever make is the CU, it should be the same make components. So is it same for SPDs. I am asking this because there is huge difference on price of SPDs between different Makes?
Should I also go with AFDD as that provide additional protection too?
Thanks for all your help

If you are quibbling about the cost of installing SPDs then the price of AFDDs will blow your mind!

AFDDs are more of an unproven and unknown quantity. SPD technology has been around for a hell of a long time and it is well understood.

Don't waste time trying to mix and match manufacturers - you can get a full RCBO board with SPD included for not a lot of money. Check out 'Fusebox' as one make that people seem pretty positive about.
 
Is Schneider fine or should I get the MK brand sockets.
Both are good but NOT the MK "essentials" range, they are utter rubbish and not even cheap enough to justify them!

My own choice has bee the MK Logic Plus range as they are sufficiently bland smooth white appearance not to seem out of place in most situations, and still have a pleasing feel/action/quality for a fair price. Also the switched Logic Plus 13A sockets are double-pole switches, not all are as the minimum requirement is SP switching when present.

Others on this forum will have favourites as well, but do chose one of the better brands as it is worth the odd quid extra per accessory.
 
I’ve read right through this thread, and I have to concur with some of the points regarding rcd protection.

changing a board means having to work on every circuit, and protect with an rcd if required.... and newest regs require almost every circuit to be rcd protected.

To suggest replace an rcbo with an mcb is the modern equivalent of replacing a fuse with a nail to stop it blowing

I might be wrong here, but would your gas pipe be plastic coated copper rather than just plastic? Meaning it will need bonded.
Water pipe could well be plastic though.
 
I don't know which MK type sockets we have. I just know that in the middle of the faceplate there is MK in a circle. I will look at the MK logic plus range.

I don't know about fuse box for SPD but looked at Wylex and that adds £75 more for SPD. The BG SPD is about £38 but a lot of people say don't go with BG. How is Fusebox in comparison to Wylex and Hager. The CU box itself is just a metal box and I don't think there is much difference between the different makes other than the cut outs etc. The actual difference is in the components going inside the CU.

I really don't get that why SPDs weren't made compulsory? Why majority of consumer boards being sold, don't have one?
The other point is about type A and AC RCD)RCBOs. There is no difference in price and type A offers better protection as it can deal with residual DC and still a lot of sellers are selling pre populated CU with type AC RCD/RCBOs. I even heard that a few European countries actually have banned type AC RCD/RCBOs.
One hand I am better off having the knowledge now and on the other hand a lot of questions in mind, why this, why not that and then I think I was better off when I didn't have this knowledge.
Thanks
 
I’ve read right through this thread, and I have to concur with some of the points regarding rcd protection.

changing a board means having to work on every circuit, and protect with an rcd if required.... and newest regs require almost every circuit to be rcd protected.

To suggest replace an rcbo with an mcb is the modern equivalent of replacing a fuse with a nail to stop it blowing

I might be wrong here, but would your gas pipe be plastic coated copper rather than just plastic? Meaning it will need bonded.
Water pipe could well be plastic though.
I know that changing to MCB without RCD isn't the right thing as it takes away the protection which we are trying to get. For me then there isn't any point upgrading from wylex plug in mcbs to slightly different type of MCB. So no we won't do that.

Inside the house the water and gas, both are copper. Outside it is plastic . The plastic gas pipe was inserted in the existing metal pipe from the street. The same with water pipe. It is about few foot in plastic from the meter and then connects to a flexible lead pipe, going in to the house. The lead pipe is then connected to a copper pipe under the kitchen floor boards.

There is only about 2 meters of visible gas pipe, where the meter is, rest is all hidden. As far as water pipe is concerned, no visible part in kitchen. The visible water pipe in the bathroom is copper but under the floor boards it was changed to plastic some 10 years back so there is no continuity to the main water pipe.
Thanks
 
If you still have a section of lead water pipe in use, I would get that replaced ASAP.
It's definitely lead pipe from outside into kitchen under floor. I remember seeing it when kitchen was fitted. Thames water should have known this as well when they changed to plastic pipe. Its about an inch in diameter and one can bend it easily.

No one ever said it should be replaced and now if we try to do it is going to cost thousands. Tiled floor in the kitchen, laminate in the hallway then the stairs in to the house and then the drive. Dig up, change the pipe then put back everything back to its original position.

Btw why it should be changed. Are there any health issues? Do you know if there were any guidance or instructions issued? I understand that I am responsible for the water pipe from the street boundary to my house so Thames water won't do it.
Thanks
 
It doesn't necessarily need to follow the same route, or end up at the same place inside. I obviously don't know the specifics of your house, but there's often an alternative route.
 
It's definitely lead pipe from outside into kitchen under floor. I remember seeing it when kitchen was fitted. Thames water should have known this as well when they changed to plastic pipe. Its about an inch in diameter and one can bend it easily.

No one ever said it should be replaced and now if we try to do it is going to cost thousands. Tiled floor in the kitchen, laminate in the hallway then the stairs in to the house and then the drive. Dig up, change the pipe then put back everything back to its original position.

Btw why it should be changed. Are there any health issues? Do you know if there were any guidance or instructions issued? I understand that I am responsible for the water pipe from the street boundary to my house so Thames water won't do it.
Thanks

Makes sense to remove the lead pipe due to the obvious health risks it poses.

Having said that my Nan's house had lead piping all the way up the drive, through the yard and throughout the house and she lived to be 100.
 

Reply to New CU and meter tails etc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looks very strange to me. Obviously had a new fuse carrier fitted to it at one point but the two cables on the left go to the meter as normal...
Replies
3
Views
725
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
881
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
458
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
847

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock