D

dokkan1080

Is a board layed out like this correct for an eco 7 off peak supply and a peak supply?

Two isolators that feed seperate rcds.

They have a shared neutral which is split at a Hanley block.

The peak live, neutral and earth enter the cu via one gland,

And off peak live and neutral enter via another with no earth eddy currents?

They have split neutral bars but share the same earth bar...

See badly drawn picture.
20210924_094455.jpg
 
For those with bad necks


E7 cons unit.jpg
 
  • Like
Reactions: loz2754
A single isolator in the board to isolate both supplies

Common MET and separate neutral bars

That's the way I always did them anyway
 
A single isolator in the board to isolate both supplies

Common MET and separate neutral bars

That's the way I always did them anyway
Wouldn't you need a 3 or 4 pole isolator for that?
Or do you mean for an installation where the switching/timing is done by the loads, not by the meter?
 
  • Agree
Reactions: pc1966
Wouldn't you need a 3 or 4 pole isolator for that?
Or do you mean for an installation where the switching/timing is done by the loads, not by the meter?
Ya in the UK you probably would if you're breaking all the live conductors
 
  • Like
Reactions: pc1966 and Avo Mk8
Fusebox do a dual tariff CU that can be configured as per your sketch.

nobody's said "No" yet ?

For the off-peak feed in, as long as L + N go through the same hole, the fact that E doesn't is not a problem, given there shouldn't be much current flowing in it!
 
Fusebox do a dual tariff CU that can be configured as per your sketch.

nobody's said "No" yet ?

For the off-peak feed in, as long as L + N go through the same hole, the fact that E doesn't is not a problem, given there shouldn't be much current flowing in it!
I see , 2 DP isolators

That wouldn't be allowed here for 2 supplies into a distrution board .
 
I see , 2 DP isolators

That wouldn't be allowed here for 2 supplies into a distrution board .
It's allowed in the UK as long it's clearly labelled that there are 2 separate supplies and that both need to be switched off.
 
  • Like
Reactions: Mikegh
It's allowed in the UK as long it's clearly labelled that there are 2 separate supplies and that both need to be switched off.
I suppose ya

Wouldn't a 4-pole be simpler with no labels needed
 
I would agree that you really want a single point of isolation for everything, so if it were me I would look at using a 4P switch (even if one pole is unused, depending on just where it is located.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Off peak and peak consuker unots combined?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
dokkan1080,
Last reply from
pc1966,
Replies
10
Views
5,103

Advert