No they are relevant to inrush currents in inductive loads, not sustained overloadsIf we were to use a 'C' Type or a 'D' Type circuit breaker; given that the I2 values of all 'Types' of circuit breaker of the same nominal current value are identical, could we then claim to have also fulfilled our primary objective of protecting an electrical circuit from 'a small overload of a long duration'?
Not all need to have a device providing protection against overload.All circuits must be protected against 'a small overload of a long duration'.
Through correct design...All circuits must be protected against 'a small overload of a long duration'.
First; you will need to provide an example of an electrical circuit that apparently does not need to be protected against 'a small overload of a long duration'.
Second; you will need to explain to all of the technical boffins at every circuit breaker manufacturer, why their 'C' Type and 'D' Type circuit breakers fail to protect an electrical circuit from 'a small overload of a long duration' and therefore aren't fit for purpose.
All circuits need to be protected from 'a small overload of a long duration'.The type of circuit breaker is not applicable to a small overload,it just determines the amount of current required to trip Instantaneously.
The best way as stated is to design the circuit correctly
All circuits need to be protected from 'a small overload of a long duration'.
Where exactly did you establish that?