Hi guys,
Went to see a property today.
Just wanted to clarify the supply type with you.
I believe it's overhead tns but others have told customer it's overhead tt.
Could you share your thoughts?
There are 3 incoming cables that come from above the house and run down into the suppliers equipment.
As they are supplying the earth I believe it is overhead tns
Picture attached as a picture paints a thousand words
Difficult to tell from that blurred picture :)
The only way to be sure is ask the DNO, they might even change their supply cable and convert to TN-C-S?
Dno wouldn't comment. They said they can provide an upgrade to pme at cost to the customer.
If it's overhead tns as I suspect then I see no reason to force additional cost to customer to change to pme...
The dno definitely are supplying 3 seperate cables to the house. Whether they have them as tns or tncs is impossible for me to say really?
The fact they are providing 3 wires rules out overhead tt? There is definitely no rod at the property as the only means of earthing is throigh the dno supplied cable...
Grrr
It was only a brief look and I didn't take a Ze as I'd have needed a ladder.
No up front rcd, I had a Zs on sockets of 0.51.
Overall I'm airing on side of tns or tncs and ruling out overhead tt (based on them providing 3 cables).
Dno say they have no idea and we're just interested in charging to change to pme
Hi - agree 3 cables and looks like TNS, perhaps check Ze and if between 0.35 and 0.8 then most likely TNS ?
Edit : tooo slow typing, with 0.51 Ze it ain't TT and afaik it's too high for their own stated target for PME.
Grrr
Have you done a loop test L-E & L-N this gives usually a good indication
i would have thought TNS to.
Have a look at the poles, some of them in my village you can see every few poles dogged down to Tera Firma. But it's probably not PME if the DNO is trying to sell you a conversion.
Edit: Wilko's got it in the bag.
Hi wilko,
0.51 is the rfc Zs not the Ze. Was unable to take a Ze due to lack of ladder. Will take that when there next.
As dno is supplying 3 cables and as they are trying to sell pme I'm going to go with tns.
Dno are really not as helpful as they should be!
The roof of the house with 3 cables. All properties on the street appear to be the same, 3 cables coming from the roof of house down the exterior wall and into the dno equipment as per the picture
Reply to Overhead tns in the UK Electrical Forum area at ElectriciansForums.net
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
5K
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
4K
I found this in a property today, I've never seen the incoming cable to the head (above and the other side of this wall) just dangling in free...