Hi there, was at a 3 phase DB today doing an EICR with another spark, there was a 10amp mcb with 1x 1.5mm2 PVC twin clipped direct feeding 4 high bay lights via a normal 10 amp switch the other spark then got his note pad out and wrote no overload protection iam say there kind of thinking a mcb protects against overload iam still an apprentice in my last year but I thought it was strange thanks in advance guys ?
 
maybe his thinking is that the 10A MCB will not protect the 10A switch from overcurrent???
 
I can't see the issue here. The MCB is no more than the switch, and the cable is going to be at least 10A but any of the usual methods (OSG Table 7.1(ii)), in fact 16A in this case. So for me that is fully overload protected, unless the "clipped direct" cable is in a very hot environment.

If the cable is massively long then it might fail on fault protection (i.e. end of cable Zs not enough to guarantee <= 0.4s disconnection) but unless it is some weird choice like a D-curve that is going to be quite long, at least 52m for B-curve (OSG table 7.1(i) as too lazy at this point to try and compute a length-limit).
 
I can't see the issue here. The MCB is no more than the switch, and the cable is going to be at least 10A but any of the usual methods (OSG Table 7.1(ii)), in fact 16A in this case. So for me that is fully overload protected, unless the "clipped direct" cable is in a very hot environment.

If the cable is massively long then it might fail on fault protection (i.e. end of cable Zs not enough to guarantee <= 0.4s disconnection) but unless it is some weird choice like a D-curve that is going to be quite long, at least 52m for B-curve (OSG table 7.1(i) as too lazy at this point to try and compute a length-limit).
Thanks a lot mate, that answer has put me on the straight and narrow this is just for my own learning great to get a second opinion from other people ?
 

Reply to Overload protection on lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Got called out to a shower tripping which has been recently installed by another spark. 8.5kw shower newly installed on existing 6mm2LSF cable...
Replies
15
Views
2K
Good morning hope everyone is staying safe. I have a question for some of the more experienced sparks, I have a client that wants her outdoor...
Replies
2
Views
4K
Am currently pondering the following situation: - Single phase PVC board, domestic, in an area where TN-C-S is the norm (underground supply etc)...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock