K

karlr

Hi Guys,
Wonder if any one can help me, I have been offered a periodic inspection at an office block where it is not possible to turn off certain circuits and working out of hours is out of the question due to files that are kept in the building.
Does anyone know where I stand with not doing any dead tests on certain circuits?

Thanks Karl per
 
There is a Limitations section and also agreed extent with customer section on a EICR form, which you can fill in. But this may lead to a very irrelevant EICR if you are not careful due to the limited inspection and testing you will be able to do.
 
  • Like
Reactions: 3 people
Some of these companies that have this issue have a regular testing regime in place and circuits that you can't fully test at this point in time get tested at other times , I would ask if this is the case , but as Dilb says it is still a case of limitations issue for you're own testing...

I would ask for and check any previous testing paperwork , and advise client accordingly..
 
  • Like
Reactions: 1 person
Hi Guys,
Wonder if any one can help me, I have been offered a periodic inspection at an office block where it is not possible to turn off certain circuits and working out of hours is out of the question due to files that are kept in the building.
Does anyone know where I stand with not doing any dead tests on certain circuits?

Thanks Karl per

If the percentage of circuits that can't be de-energized renders the EICR not worth the paper it's written on, consider this ...
Can they arrange out of hours security to follow you around to prevent you poking your nose into their precious (and most probably, totally boring) files?
That way, you can carry out a full Inspection and Test.

I've done a couple of Inspections that way in the past.
 
  • Like
Reactions: 4 people
And even if it has a regime of maintenance and subsequent testing, make sure it is not the same tame circuits that have been tested over and over again.
 
Hi Guys,

Does anyone know where I stand with not doing any dead tests on certain circuits?

Thanks Karl per

You can't do what you can't do, so just get on with the rest of the testing etc etc

Unless you don't fancy the job, then hand it back.
 
Thanks for all the info much appreciated, the installation is around 10yrs old but they have no previous records.


Thanks again
 
Thanks for all the info much appreciated, the installation is around 10yrs old but they have no previous records.


Thanks again

So it's even more important that this installations ''First'' EICR is carried out properly without needless Limitations being applied.
 
  • Like
Reactions: 1 person
So it's even more important that this installations ''First'' EICR is carried out properly without needless Limitations being applied.

Agreed. I take it no EIC either? But, if the client are instructing to limit the testing due to operational reasons then list them, attach a cover letter to the EICR saying that you stongly advise a full EICR to be carried out along with the reasons why and there is nothing more that can be done.

We cannot tell our clients how to spend their money. We can only advise on what we feel is required.
 
  • Like
Reactions: 1 person
i would have a word with the client about doing dead tests on select circuits (anthing that needs power can be temporarily powered by another circuit during test)

it should be possible to do the full eicr in parts like this as long as the customer is willing

otherwise your going to have plently of LIM on test sheets
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
periodic inspection where power can not be turned off
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
karlr,
Last reply from
shanky887614,
Replies
10
Views
1,576

Advert