I am just going to get the regs out shortly, however anyone done any work on petrol station pump supplies, as part of a refurb in commercial premises I will be fitting a new CU for the shop and forecourt a heads up on anything likely to be a pain would be great cheers
PIct
 
compex would be required if doing any of the pumps
there are specific regs covering petrol stations cant mind right now what they are tho
 
I have just had a look through the regs I cant find any mention of petrol stations, I could have sworn there was a section on it after marinas etc, any one knows where it is, cheers all, also when doing the I&T is ther differant IR requirements ?? and where is the firemans switch in the circuit?? anyone ??
Pict
 
You need to consult locally about this, once you have read BGB Appx 2, halfway down page 293, item number 5.

Cheers............Howard
 
I have had a trawl on the net, your right about compex Mogga, so I will be limiting my involvment to the shop and leave the forecourt to a compex qualified spark, luckily I can supply the shop totally seperate from everything else
P
 
  • Like
Reactions: 1 person
Cheers for that Howard, to be honest I was swithering on the matter, I think I will let the owner phone the local authority for guidance on this
Pict
 
I have had a trawl on the net, your right about compex Mogga, so I will be limiting my involvment to the shop and leave the forecourt to a compex qualified spark, luckily I can supply the shop totally seperate from everything else
P

I agree with what you are saying. I know, you know and we all know that this is just a shop, just like any other shop, and it unlikely to throw up any problems, but. I would still have a gander at the rules and regs surrounding this, as even though it is just a shop, it is still in an environment that stores combustible material, by your own admission it is a new environment for yourself, so make sure you dot the i's and cross the t's for your own piece of mind.

Cheers..........Howard
 
Yep I was down there today for diesel and it is amazing what you see when you actually look LPG cylinders and fire wood outside the door,
usuall shelves filled with oils and brake fluid, yep definately worth some thought, I did open the book honest Biff
Pict
 
As far as I'm aware, the shop is considered separate from the forecourt, and BS7671 applies.
 
Your most likely correct Spin, I was thinking that the propritor of the business is responsible for what he puts where under the term of H&S etc
Pict
 
You need the APEA Blue book for the Regs on forecourts.
The installation comes under the control of the L.A Petroleum Officer.

The kiosk is outside of any controlled zone, normal regs apply except for the installation of E.M stop circuit for the pumps.
This is normally a contactor isolating all supplies to the pumps reset only from the kiosk and has Stops on the cashiers desks, at the tank fill point and the Firemans switch is in this circuit.
The Firemans Pump control switch is on the forecourt so has very specific regs re siting and labelling.

Best advice, keep away from the pump supplies, but for the future keep an eye on how the pump supply install is done.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

the pict

Mentor
~
Joined
Location
Brodick
Business Name
Devlin Maguire Electrical

Thread Information

Title
petrol stations
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Thread Tags

Tags Tags
petrol

Advert

Thread statistics

Created
the pict,
Last reply from
worzol99,
Replies
12
Views
7,429

Advert