Discuss RCCB as main switch? in the UK Electrical Forum area at ElectriciansForums.net

N

Noob2013

Hi all,

I have been to a property where the tails come out of the meter and into an RCCB which then feeds the main switch of the consumer unit. All circuits are protected by MCBs.

If I'm adding a new circuit, is it best put in an RCBO instead of an MCB?

Thanks
 
There should not be a 'front end' RCD installed at all. Circuits should be separated so that if a fault occurs the whole installation does not trip.
 
There should not be a 'front end' RCD installed at all. Circuits should be separated so that if a fault occurs the whole installation does not trip.

Yes lets rip it all out and start from a fresh.. and then also get rid of the 100mA time delay RCD's from them old installs lol
 
Hi all,

I have been to a property where the tails come out of the meter and into an RCCB which then feeds the main switch of the consumer unit. All circuits are protected by MCBs.

If I'm adding a new circuit, is it best put in an RCBO instead of an MCB?

Thanks
Hi Noob,

A new circuit would need notifying under Part P of the building regs. As your profile shows that you're an apprentice you could maybe undertake this job with one of the electricians that you work with.

Also, if you don't already have it, get yourself access to the trainees forum.
 
There should not be a 'front end' RCD installed at all. Circuits should be separated so that if a fault occurs the whole installation does not trip.
cobblers. this was most likely to regs. when installed. there's no requirement to bring it up to current regs. although any work done on the installation must comply to 17th.
 
cobblers. this was most likely to regs. when installed. there's no requirement to bring it up to current regs. although any work done on the installation must comply to 17th.

"most likely"

good enough for you. Not good enough for me.

As soon as he disconnects the tails to the existing he must be happy with the current installation before he reconnects it.

Just my opinion.
 
"most likely"

good enough for you. Not good enough for me.

As soon as he disconnects the tails to the existing he must be happy with the current installation before he reconnects it.

Just my opinion.

as long as it's safe for continued use. the fact that it was installed to a previous version of the regs. is no reason to condemn it. that's like condemning a 1990's car because it doesn't have abs or airbags.
 
Hi Noob,

A new circuit would need notifying under Part P of the building regs. As your profile shows that you're an apprentice you could maybe undertake this job with one of the electricians that you work with.

Also, if you don't already have it, get yourself access to the trainees forum.

Can't we have an "Apprentice" badges Mods?
 
as long as it's safe for continued use. the fact that it was installed to a previous version of the regs. is no reason to condemn it. that's like condemning a 1990's car because it doesn't have abs or airbags.

Not condem but advise and make sure it is on the cert if the home owner does not want it.
 
New posts

Reply to RCCB as main switch? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
452
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
815

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock