When I do a loop test on an installation protected with an rcd using my robin kmp 4118 (no d lock) the rcd doesnt trip.
Both the tester and rcd have been tested ok by other means - any ideas?
Thanks
A very frustrated engineer
 
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Advertisement - Content continues below
aslong as it trips with the rcd tester i doesnt matter making it trip through the loop tester is pain anyway not something you need to worry about when it doesnt happen.
 
S

Spudnik

  • Thread Starter Thread Starter
  • #3
Agree with Mark on that.

Some manufacturers RCD's or RCBO's wont trip when loop testing.

If they do trip, then the only option normally is to bridge out the RCD temporarily.
 
A

AMST09

  • Thread Starter Thread Starter
  • #4
Agree with Mark on that.

Some manufacturers RCD's or RCBO's wont trip when loop testing.

If they do trip, then the only option normally is to bridge out the RCD temporarily.

RCDs aren't supposed to be bridged out, if the RCD trips the value should be calculated using
Zs=Ze+R1+R2 and then noted on the test sheet
 
S

spark1

  • Thread Starter Thread Starter
  • #5
As long as you are confident the RCD AND the Loop tester are functioning correctly then I cant see any problem.
As the above post states Zs can be obtained by calculation ,and in fact in some cases to prevent Live Working... this is the only acceptable method to use.

spark1
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to RCD problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
Advertisement - Content continues below
Top Bottom