If the shower is tripping when it is not in use then its would lean more to a faulty cable/connection due to the fact there is no load being used surely ?
Therefore check all connections you can access, do IR test then r1 + r2 see if any reading look out of place!

Zs test will probably not tell you that much in relation to the fault !
Has the shower been working for a while and this falut just appeared?
 
If the shower is tripping when it is not in use then its would lean more to a faulty cable/connection due to the fact there is no load being used surely ?
Therefore check all connections you can access, do IR test then r1 + r2 see if any reading look out of place!

Zs test will probably not tell you that much in relation to the fault !
Has the shower been working for a while and this falut just appeared?
(R1 R2) before IR to ensure all portions of the circuit are being subjected to the test
 
yep shower was installed 6 years ago yea so if i disconnect the loads side and do a IR test if i get anything under >200mohms theres a cut or something in the cable?
 
yep shower was installed 6 years ago yea so if i disconnect the loads side and do a IR test if i get anything under >200mohms theres a cut or something in the cable?
get continuity first....then IR....
continuity does what it says on the tin....
IR demonstrates dielectric strength....
 
He must of packed up and gone home, I can't wait until the fault is discovered and revealed to us all.
 
He must of packed up and gone home, I can't wait until the fault is discovered and revealed to us all.

hi guys im going back there on friday so ill tell you what i discover then thanks for your input, hopefully i find the fault ha!
 
After performing ALL tests were the results satisfactory?
yes...one thing i`v noticed in here with these kind of threads is the persistant lack of basic proofing (by testing) of offending circuit/s & apperatus/connected loads....
 
Yes it makes you wonder Glenn if some of the sparks on here either own a MFT or know how to use one lol
well i`d be using that term loosely Mike if they arn`t in ownership of the necessary equipment to carry out the job in a compliant manner.....
 
If I'd of asked the question, I'd of at least started of by stating "I'm stumped" I've done this, this and this and I can't get my head round the problem please help lol..................
 
If I'd of asked the question, I'd of at least started of by stating "I'm stumped" I've done this, this and this and I can't get my head round the problem please help lol..................
except you wouldn`t be stumped Kas....
 