Re: RCD trip after board upgrade. Frustration who on my side? Who's on landlords? A r

Yeah thats about it.

I wouldn't check appliances on an EICR, but after changing a CU and adding RCD protection I do check that the important appliances all work without tripping RCD's, Fridges and freezers, oven, immersion, boiler, kettle (naturally the most important ;) )
Maybe I should rethink my standards as I've always only checked the kettle :)
NB I'm not saying I use the kettle as an installation tester :)
 
Re: RCD trip after board upgrade. Frustration who on my side? Who's on landlords? A r

I think what Dave means is that if you'd done a functional test on the oven you might have found it before all this but I have to say, if I'm doing a domestic EICR I don't go round checking the appliances so I'd have missed this one too.
Yer but who turns ovens on for 20 minutes to check lol I see what you are saying.
 
Re: RCD trip after board upgrade. Frustration who on my side? Who's on landlords? A r

Of course, if it looked like a dodgy secondhand oven that's been stood dormant in a damp shed for years before the landlord bought it, I could suggest turning every element up to max, whipping out the earth conductor and standing well clear! Lol
after 5-10 mins the fault may clear... And at the worse there would be a bloody great hole in the faulty element or the remnants of a faulty stat controller splattered around the kitchen ;-)
..... But obviously that is well outside the scope of bs7671 ...
Haha that made me laugh.
 
Re: RCD trip after board upgrade. Frustration who on my side? Who's on landlords? A r

Yeah thats about it.

I wouldn't check appliances on an EICR, but after changing a CU and adding RCD protection I do check that the important appliances all work without tripping RCD's, Fridges and freezers, oven, immersion, boiler, kettle (naturally the most important ;) )
There was nothing there only the oven and it originally took 20 minutes to trip, would you have seriously stood there waiting for 20 minutes!
 
Re: RCD trip after board upgrade. Frustration who on my side? Who's on landlords? A r

Well I was under the impression you test to the age of the installation, ie both works were carried out and should of been put on an RCD. Also maybe I am wrong, but who puts satisfactory when there is an electric shower with no RCD, just sends a shiver up my spine. I thought at the end of the day it comes down to the testers professional look at the regs are a guide.

Could I have said satisfactory then you think?


No you inspect and test to the current version of the regulations, and code accordingly. New works which don't comply receive the same codes as 30 year old installations with teh same non-compliances.
 
Re: RCD trip after board upgrade. Frustration who on my side? Who's on landlords? A r

No you inspect and test to the current version of the regulations, and code accordingly. New works which don't comply receive the same codes as 30 year old installations with teh same non-compliances.
So a shower just on a mcb you would code c3?
Looks like I am too harsh then.
 

Reply to RCD trip after board upgrade. Frustration who on my side? Who's on landlords? A rant! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
25
Views
1K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
903
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock