We are not talking of a particular circuit type here and I agree that lighting and power circuits would not be an issue due to true usage but taking your shower that has a cable route through a full height wall and a little bit more, if 10mm
64amp clipped direct
32amp just stuffed in't middle of it all
44amp in some sort of conduit in't middle of all the insulation.
That's the difference between a nice powerful warm 9.5kw for me and a piddly 7.5 kw for you. There is something in it for fixed loads.
 
We are not talking of a particular circuit type here and I agree that lighting and power circuits would not be an issue due to true usage but taking your shower that has a cable route through a full height wall and a little bit more, if 10mm
64amp clipped direct
32amp just stuffed in't middle of it all
44amp in some sort of conduit in't middle of all the insulation.
That's the difference between a nice powerful warm 9.5kw for me and a piddly 7.5 kw for you. There is something in it for fixed loads.
Am I missing something, how does the ccc increase by 12A because the cable is contained in conduit.
 
Look in the tables - it gets reduced from 64 to 44 if contained and in insulation but reduced from 64 to 32 if placed just in insulation. Come on westward did you have a heavy lunch?
 
Putting on my tin hat, I reckon the good book says no advantage for using conduit in insulation, advantage comes from clipping cable or conduit to the wall. Little pic to illustrate :

IMG_0361.JPG
 
Okay you are looking at Table 4D5. Your 44A comes from column 7, enclosed in conduit in an INSULATED WALL. Your 32A comes from column 5, in a stud wall with THERMAL INSULATION. Column 7 does not refer to thermal insulation it refers to an insulated wall. None of the Installation Methods in that table refer to cables in conduit surrounded by thermal insulation. Your sums are incorrect.
 
Putting on my tin hat, I reckon the good book says no advantage for using conduit in insulation, advantage comes from clipping cable or conduit to the wall. Little pic to illustrate :

View attachment 33743
Was just looking at the same thing, but it refers to a thermally insulated wall much like column 7 Table 4D5. So from your shown Table you would refer to column 2 in 4D2A which give an amp or so is the same as 4D5.
 
Okay you are looking at Table 4D5. Your 44A comes from column 7, enclosed in conduit in an INSULATED WALL. Your 32A comes from column 5, in a stud wall with THERMAL INSULATION. Column 7 does not refer to thermal insulation it refers to an insulated wall. None of the Installation Methods in that table refer to cables in conduit surrounded by thermal insulation. Your sums are incorrect.

Yes it does. Column 7 reference method A* for full installation method refer to table 4A2 number 2 but for flat twin and earth cable.

4A2 number 2 multicore cable in conduit in a thermally insulated wall with an inner skin having a thermal conductance of not less than 10 W/m2K c. So you use reference method A to determine CCC.
 
Last edited:
Yes it does. Column 7 reference method A* for full installation method refer to table 4A2 number 2 but for flat twin and earth cable.

4A2 number 2 multicore cable in conduit in a thermally insulated wall with an inner skin having a thermal conductance of not less than 10 W/m2K c. So you use reference method A to determine CCC.
I can see your point but it does not refer to thermal insulation but a thermally insulated wall. Not going to cross swords here my initial confusion was from an earlier post which stated containing the cable in conduit would increase the ccc, and I assume the poster was misguided by Table 4D5.
 
To add my measly morsel, 7.1 Reference method A, is described as 'wall consists of outer weatherproof skin' etc etc, which suggests to me is for an external wall. Whereas Reference method 102 - 103 are referring to stud walls, and placing in conduit will have no beneficial or detrimental effect to ccc, apart from bunching of cables?

OR should I just carry on cooking me piece of beef :rolleyes:
 
Beef in. Most of the wood stud work installations I've seen or done have the cables down the middle of said stud work and would never be close to the inner wall surface.
 
Beef in. Most of the wood stud work installations I've seen or done have the cables down the middle of said stud work and would never be close to the inner wall surface.
No Mate run it in some trunking or conduit that will increase the ccp of the cable.
 
Spuds in. You've confused me now Pete, thought the whole thrust of this debate, suggest no benefit of putting cables in conduit in insulated stud wall?
Trying to be sarcastic, but obviously it didn't work
 

Reply to Reference Meathod for Timber Frame in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
Hi guys After some suggestions. My next job will be to wire a new timber frame extension throughout. My questions are any tips for running...
Replies
6
Views
1K
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
906
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
786
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
994

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock