Hi guys,

I am just trying to price a job up, which I am a bit unsure of. It is at a commercial premises, the supply I have got is 300a three phase, with ruffley 150a - 200a per phase already being used. The customer has asked me to run a supply, 300m (buried) for a 50kw load. It will supply staff living quarters, like a three storey house, and also possible expention in the future.
I have calculated the cable to 70mm2 SWA, 4core, with a 50mm2 earth. Do you think I should still put a earth rod in at the load side, house side?
Also a bit in unsure on protection, I calculated 125a 60947-2?
And then I was thinking of splitting the phases for each floor at the house, so ground floor L1, 1st floor L2 + 2nd floor L3?
Any help will me much appreciated
 
first thoughts here are would it be better to have a separate new supply?
 
i'll do it for 27.5k. bankers order to my offshore account.
 
What ever size cable it doesn’t matter. By asking on here you show you’re out of your depth completely. How did you get to quote for this job?
 
  • Like
Reactions: 2 people
I am a qualified electrician, and just trying to get a few small jobs going, before I start on my own next year. Only asking for a bit of advice
 
In your original post you said 50Kv and now in your new post is 50kW?!

Sent from my GT-P7510 using Tapatalk 2
 
Just a warning mate. If you are qualified, but presumably working for someone else atm, do you have public liability in place just in case something were to go wrong?
 
Though nothing to add to the thread, I just want to know where you have been G, I never had a note from ya mum excusing you
 
Kibble, I know nothing about 3-phase but I know if I were to use one phase for each floor of a dwelling then I would have 400v between Lines in the ceiling.

Laurie
 
Hi guys,

I am just trying to price a job up, which I am a bit unsure of. It is at a commercial premises, the supply I have got is 300a three phase, with ruffley 150a - 200a per phase already being used. The customer has asked me to run a supply, 300m (buried) for a 50kw load. It will supply staff living quarters, like a three storey house, and also possible expention in the future.
I have calculated the cable to 70mm2 SWA, 4core, with a 50mm2 earth. Do you think I should still put a earth rod in at the load side, house side?
Also a bit in unsure on protection, I calculated 125a 60947-2?
And then I was thinking of splitting the phases for each floor at the house, so ground floor L1, 1st floor L2 + 2nd floor L3?
Any help will me much appreciated

Whats the earth rod for?? is it a TT installation? and if you ran a new submain in the new DB would be TNS...... you need to work out the load on the new Db, amount of sockets, lights etc, the diversity, to design a building you work back from the power required, that determines the size of board needed, which determines the size of cable feeding it, once you have that, then you will look at spare capacity in the existing board, and 3 phase installations are not designed by simply throwing one phase per floor!! you will need to balance the phases, which means looking at which parts will be used the most, and if you have say 2 socket circuits within touching distance they need to be on the same phase, and lights, if you have 2 way lighting for example with 2 circuits in the switch, again, same phase, all the while thinking about the same load being on each phase, protection - if it was me the new submain would be 100mA protected, then drop to 30mA for sockets etc... housebashing it aint.... regs will give you the cable sizes needed, dont forget grouping factor, (if needed) derating factor for ambient temp, (if needed), and volt drop, if you are using SWA - eland cables website do great easy to follow data sheets,

like i said you will have to work back, if the guy wants a price then a true price would involve 1- 2 days design on the new building just to work out the power requirement.....
 
To be honest guys I can't really see why we would be so concerned with a lighting circuit on one phase in a commerical environment being run next to a RFC on another phase.

I could see in a domestic situation you try your best to have perhaps one area on one phase and not have the chance of 400 volts in close proximity, but even in the best designed and run installation, there is going to be somewhere in it that phases are close together, the main intake for one and sub mains feeding boards for another
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Running of SWA, sub main
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
kibble19,
Last reply from
Engineer54,
Replies
20
Views
3,539

Advert