Discuss Solar 3 phase kva limit in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
0
My client wants to install a 100kw solar system. He has 3 phase and 100 amp fuse installed on 200kva transformer.
Is 69kw the limit on 100 amp fuse or can he go over without a limiter fitted?
Thanks
 
You will have to plan for all eventualities. So lets say batteries, if any, are fully charged, the property loads have dropped to low, EV's are fully charged etc, this typically happens on a Sunny, warm day. So an export controller will be the only way to stop the supply fuse blowing. You may also find the DNO will have a view on export limit as well, which may be lower than the fuse size.
I have installed a 56KW system on a TP 100A supply and i have limited the output to 11KW feed-in.
 
You will have to plan for all eventualities. So lets say batteries, if any, are fully charged, the property loads have dropped to low, EV's are fully charged etc, this typically happens on a Sunny, warm day. So an export controller will be the only way to stop the supply fuse blowing. You may also find the DNO will have a view on export limit as well, which may be lower than the fuse size.
I have installed a 56KW system on a TP 100A supply and i have limited the output to 11KW feed-in.
I’m sure DNO have said 23kw per phase. Which is 69kw. I will speak to them. I think an export controller will be the best option. The inverters usually have built in export limits but if the limit is set on the inverter at 69 kw and the property use 9 kw does that mean only 60kw goes back into the grid? or is it better to have a separate export controller and set that at 69kw so They can export the maximum amount set by the DNO?
What happens if we limit it at 80kw, will the fuse blow?
 
Check the inverter specs or post the model, if the inverter spec is suggesting a CT clamp on incoming tails, then its likely it can monitor grid export and control at that point, so the property can consume as much as it likes, the whole 100KW if necessary with the inverter just backing off when it sees excess feed in. Don't design it to push the fuse over 100amps, its pretty damaging when they blow to all equipment in the property and DNO may get fed up coming out to replace it. It it were me i would set the export limit to either DNO stipulation or if they are silent probably around 75 amps max. The inverter has to maintain stability so export limits often go slightly over or under , its not an exact tracking of output. In addition, unless you are getting substantial feed in tariffs from energy company, there is no point exporting the maximum, the inverter will be less stressed if it is limited.
 
Check the inverter specs or post the model, if the inverter spec is suggesting a CT clamp on incoming tails, then its likely it can monitor grid export and control at that point, so the property can consume as much as it likes, the whole 100KW if necessary with the inverter just backing off when it sees excess feed in. Don't design it to push the fuse over 100amps, its pretty damaging when they blow to all equipment in the property and DNO may get fed up coming out to replace it. It it were me i would set the export limit to either DNO stipulation or if they are silent probably around 75 amps max. The inverter has to maintain stability so export limits often go slightly over or under , its not an exact tracking of output. In addition, unless you are getting substantial feed in tariffs from energy company, there is no point exporting the maximum, the inverter will be less stressed if it is limited.
Thanks for your input and suggestions.
 

Reply to Solar 3 phase kva limit in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi I have three phase installed recently to increase generation. DNO approved the extra 2 solar arrays so we have 3.68KW FIT on one phase and 8KW...
Replies
1
Views
690
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW...
Replies
3
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
Help please, this is my first post on this subject regarding solar panel / battery installation into house with 3 phase supply. I am a DIY level...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock