Looking to change the small consumer unit in my garage with a Hager Split Load Consumer Unit Complete with: 2x 100A Type a RCDs x 100A DP main switch. Reason I will have an EV charger fitted later in the year. One side of the split for the garage and the other side for the EV charger at a later date. There is a Hager Split Load Consumer Unit in the house with a B32 MCB, connected by an think a 6m SWA cable the garage house is 100amp rated, I am open to your suggestions, gremlin
 
Don't bother with split load, just use an RCBO board. However if the supply circuit is already RCD protected then you could just use MCBs.

But as you're planning on an EVCP you need to be aware of the requirements for specific types of RCD and have the correct one for the charger.

In this case I would recommend you employ an electrician as this is not only notifiable work there's also a lot of considerations such as DC currents from the ECVP blinding the RCD potentially causing it to not operate when needed the most.
 
Don't bother with split load, just use an RCBO board. However if the supply circuit is already RCD protected then you could just use MCBs.

But as you're planning on an EVCP you need to be aware of the requirements for specific types of RCD and have the correct one for the charger.

In this case I would recommend you employ an electrician as this is not only notifiable work there's also a lot of considerations such as DC currents from the ECVP blinding the RCD potentially causing it to not operate when needed the most.
 
Thanks Strima
I appreciate all your help? The RCBO board sounds the best choice. As the consumer unit and the MCBs RCDs and main switch are all Hager in the house, do you think I should use a Hager RCBO and MCBs etc. in the garage? What about a Hager Type 2 Consumer Unit Surge Protection Kit is that a good thing, bearing in mind the EV charger to be fitted later in the year, as there is no room in the house consumer unit.

Thanks again for your professional advice gremlin

PS yes I will employ an electrician
 
I'd say it's definitely worth consulting an electrician who installs EV points at this stage, as it may save you having to change things in a few months.

As already mentioned, RCD types will be important. But also depending on the charger you go for and the existing load in the garage, 32A may not be adequate for the supply - and whether it can be upgraded will depend on route/length/size of the armoured cable. It may even be that it makes more sense to run a separate feed for the charger when the time comes, but that is something that a good electrician can look at and advise on,.

Hager is a good brand so always a good choice, although a separate Consumer unit doesn't need to match what is there already other than for aesthetic reasons. It may be that size and availability, or even the preference of the installer may play a factor in what is chosen.

A board with RCBOs for existing circuits and space to add suitable RCD protection for the charger does seem like the most likely suitable option from what you've told us.

A Surge protection kit is a sensible addition generally (and necessary in many cases without specifically deciding against it) - however, it usually needs to be within a short distance of the source of the installation to protect it (they can go in a separate enclosure beside the consumer unit or before it). There are types that can be installed at sub boards to protect those loads only, but they usually work in conjunction with one at the source.

Getting a suitable electrician at this stage should help identify ways to do what you need now and allow for the future, with the minimum necessary expense...
 
I'd say it's definitely worth consulting an electrician who installs EV points at this stage, as it may save you having to change things in a few months.

As already mentioned, RCD types will be important. But also depending on the charger you go for and the existing load in the garage, 32A may not be adequate for the supply - and whether it can be upgraded will depend on route/length/size of the armoured cable. It may even be that it makes more sense to run a separate feed for the charger when the time comes, but that is something that a good electrician can look at and advise on,.

Hager is a good brand so always a good choice, although a separate Consumer unit doesn't need to match what is there already other than for aesthetic reasons. It may be that size and availability, or even the preference of the installer may play a factor in what is chosen.

A board with RCBOs for existing circuits and space to add suitable RCD protection for the charger does seem like the most likely suitable option from what you've told us.

A Surge protection kit is a sensible addition generally (and necessary in many cases without specifically deciding against it) - however, it usually needs to be within a short distance of the source of the installation to protect it (they can go in a separate enclosure beside the consumer unit or before it). There are types that can be installed at sub boards to protect those loads only, but they usually work in conjunction with one at the source.

Getting a suitable electrician at this stage should help identify ways to do what you need now and allow for the future, with the minimum necessary expense...
 
re. EV chargers.just seen ad. for hyundai says quick part charge for XX miles on a 350kW charger. WTF?
 
Don't bother with split load, just use an RCBO board. However if the supply circuit is already RCD protected then you could just use MCBs.

But as you're planning on an EVCP you need to be aware of the requirements for specific types of RCD and have the correct one for the charger.

In this case I would recommend you employ an electrician as this is not only notifiable work there's also a lot of considerations such as DC currents from the ECVP blinding the RCD potentially causing it to not operate when needed the most.

Looking to change the small consumer unit in my garage with a Hager Split Load Consumer Unit Complete with: 2x 100A Type a RCDs x 100A DP main switch. Reason I will have an EV charger fitted later in the year. One side of the split for the garage and the other side for the EV charger at a later date. There is a Hager Split Load Consumer Unit in the house with a B32 MCB, connected by an think a 6m SWA cable the garage house is 100amp rated, I am open to your suggestions, gremlin
 

Reply to Split Load Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
723
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock